    Question Carrier Vector 1800 reset HM



    Hi.
    I had come Carrier Vector 1800 with error 223 about need maintenance for disel.
    After our company did maintenance fully I had try delete this error with reefermanager.
    In tab "Monitor and Override operations" if I press btn "Microprocessor monitor" on end tab I can see 'Hours to disel Maintenance" = 0. How I can add to this setting additional hours? If I can, error 223 not to be in future. I can't find in Microprocessor setup this setting for change.

    Sorry for my English



  2. #2
    Join Date
    Feb 2011
    Location
    Russia (Sochi)
    Age
    38
    Posts
    6
    Rep Power
    0

    Re: Carrier Vector 1800 reset HM

    Right name of counter "Hours to Engine Maintenance" tab "Hours/cycles".

  3. #3
    Join Date
    Mar 2009
    Location
    Brisbane, Australia
    Age
    65
    Posts
    197
    Rep Power
    16

    Re: Carrier Vector 1800 reset HM

    Open the Reefer Manager help file (big blue icon) and type in "change hours".
    This will guide you through what you are trying to do.
    It is located in the "Carrier" sub-directory, in the "Program Files" directory in the C:/ root directory.

  4. #4
    Join Date
    Feb 2011
    Location
    Russia (Sochi)
    Age
    38
    Posts
    6
    Rep Power
    0

    Re: Carrier Vector 1800 reset HM

    Thank you for answer. I had read help to reefermanager in PDF and HLP. No information about this hourmeter. I have problem only with this hourmeter.
    Usually after we do Mainentance I add hour is HM1, or HM 2,3,4,5. But I never had work with this counter. HM numeric (0-5) on 0. I can add to numeric hourmeter, but can't in "Hours to Engine Maintenance".

  5. #5
    Join Date
    Jul 2009
    Location
    Latvia
    Age
    35
    Posts
    49
    Rep Power
    0

    Re: Carrier Vector 1800 reset HM

    On vector You change hours: Serial operations/Microprocessor setup/configuration - scroll down/diesel reset value.

    Some times You have to send zero first and only then 1500hrs. If You send 1500hrs only - the microprocessor does not reset - don't know why.

    Best regards, Edvin.

  6. #6
    Join Date
    Feb 2011
    Location
    Russia (Sochi)
    Age
    38
    Posts
    6
    Rep Power
    0

    Re: Carrier Vector 1800 reset HM

    Big thanks, Edvin. You real help me.

  7. #7
    Join Date
    Mar 2009
    Location
    Brisbane, Australia
    Age
    65
    Posts
    197
    Rep Power
    16

    Re: Carrier Vector 1800 reset HM

    Guys; problems with Vector controllers is not uncommon.