Klixon
This is a klixon from a Copeland Semi Hermetique Compressor
The make is KRIWAN
INT69 Auslosegerat
Art - Nr 52 A 120
AnschluB AC40 60 Hz 200 240V
zul Umgebungstemp -30 +70C
relais AC 250V max 6A 300VA ind
it has 7 terminals
I know the first two are live and neutral
Then there are numbered 1, 2, 12, 14 and 11
What I want to know is this
I know compressor is 3 Phase
What does this relay/ klixon do??
And how should it be wired?Last edited by Abe; 11-01-2006 at 10:34 AM.
-
25-09-2005, 07:26 PM #2
Re: Klixon
This person should know:
Diane Kuipers +31.546.879560 ph.
+31.546.879204 fax
d-kuipers@ti.com
-
25-09-2005, 07:39 PM #3
Re: Klixon
Live nutral, Probe out , probe in, and three relay terminals, (common, open and closed)
If memory serves there are markings on the side of the thing below the terminals. The probe terminals conect to a temp probe in the compressor head.
Hope that helps.
-
25-09-2005, 08:56 PM #4
Re: Klixon
Hi,
I think I've found it!!! Click below...
http://www.kriwan.com/produkte/splas...eich=Ie&Lang=E
-
25-09-2005, 09:26 PM #5
Re: Klixon
Thx Hitsme
This is where it is
http://www.kriwan.com/download/datei...69000046_e.pdf
-
26-09-2005, 04:18 AM #6
Re: Klixon
Hi Abe.
It is exactly as Chilly says.
If there is a problem with it, you can bridge the relay till you get a new one.
Chemi
-
28-09-2005, 10:31 AM #7
Re: Klixon
Originally Posted by chemi-cool
Chemi
Pse tell me what this device does
I know it senses temp of the compressor head or something and will cut it out if the head gets too hot
What are the relays for??
Thx........
-
28-09-2005, 03:40 PM #8
Re: Klixon
Hi Abe.
This is a motor winding protection unit, the don't last too long.
If you take a close look, you will see the the L and N.
Then you have two terminals marked 1 and 2, these are for the thermistor, then you have a relay contacts, 11 is common, 14 is NO and 12 is NC.
The relay contacts are used to protect the winding by connecting the compressor contactor in series so if the winding temp goes up, it will cut the compressor out.
One of the problems with these things is the compressor vibrations, it brake the contacts inside.
I usually install them in the electric board.
Chemi
-
28-09-2005, 07:07 PM #9
Re: Klixon
Hi Abe,
The live and neutral connections on it are ONLY for a live and neutral connection.
These connections are to power the transformer inside it.
(hope you are not trying to put the control circuit through the L & N connections)
The relay then provides a n/o and n/c contact. To which you can put 240v through it, up to 6AIF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
05-10-2005, 12:10 PM #10
Re: Klixon
Hi,
first of all - klixon is thermorelay. If temperature is too high, kontakts of klixon are off (or on) and ...
The Kriwan needs thermistor - it is resistor with resistanse as function of temperature.
You have to choose another Kriwan!
BR
Andrew
-
05-10-2005, 07:15 PM #11
Re: Klixon
Originally Posted by chillin out
I understand much much better now.......
I know now.........the live and neutral powers the transformer.
And I can use the relay to switch on and off........
Its coming together now......
Similar Threads
-
Compressor shutting down on overtemp?
By Larry2 in forum Air ConditioningReplies: 50Last Post: 01-08-2006, 11:36 PM -
Help Me !
By FRIDGE in forum Technical DiscussionsReplies: 17Last Post: 17-11-2004, 08:41 PM -
scroll compressors
By bernard in forum Supermarket RefrigerationReplies: 16Last Post: 16-09-2004, 08:31 PM -
Evap motor no come on
By Apprentice in forum Technical DiscussionsReplies: 13Last Post: 04-12-2003, 04:07 PM