    Klixon



    This is a klixon from a Copeland Semi Hermetique Compressor

    The make is KRIWAN
    INT69 Auslosegerat
    Art - Nr 52 A 120
    AnschluB AC40 60 Hz 200 240V
    zul Umgebungstemp -30 +70C
    relais AC 250V max 6A 300VA ind

    it has 7 terminals

    I know the first two are live and neutral
    Then there are numbered 1, 2, 12, 14 and 11


    What I want to know is this

    I know compressor is 3 Phase

    What does this relay/ klixon do??
    And how should it be wired?
    Last edited by Abe; 11-01-2006 at 10:34 AM.



  2. #2
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Klixon

    This person should know:
    Diane Kuipers +31.546.879560 ph.
    +31.546.879204 fax
    d-kuipers@ti.com

  3. #3
    Join Date
    Dec 2003
    Location
    uk
    Age
    51
    Posts
    62
    Rep Power
    21

    Re: Klixon

    Live nutral, Probe out , probe in, and three relay terminals, (common, open and closed)

    If memory serves there are markings on the side of the thing below the terminals. The probe terminals conect to a temp probe in the compressor head.

    Hope that helps.

  4. #4
    Join Date
    Sep 2005
    Location
    Australia
    Age
    50
    Posts
    33
    Rep Power
    0

    Re: Klixon

    Hi,

    I think I've found it!!! Click below...

    http://www.kriwan.com/produkte/splas...eich=Ie&Lang=E

  5. #5
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Klixon


  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Klixon

    Hi Abe.


    It is exactly as Chilly says.
    If there is a problem with it, you can bridge the relay till you get a new one.


    Chemi

  7. #7
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Klixon

    Quote Originally Posted by chemi-cool
    Hi Abe.


    It is exactly as Chilly says.
    If there is a problem with it, you can bridge the relay till you get a new one.


    Chemi

    Chemi

    Pse tell me what this device does
    I know it senses temp of the compressor head or something and will cut it out if the head gets too hot

    What are the relays for??
    Thx........

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Klixon

    Hi Abe.

    This is a motor winding protection unit, the don't last too long.

    If you take a close look, you will see the the L and N.
    Then you have two terminals marked 1 and 2, these are for the thermistor, then you have a relay contacts, 11 is common, 14 is NO and 12 is NC.

    The relay contacts are used to protect the winding by connecting the compressor contactor in series so if the winding temp goes up, it will cut the compressor out.

    One of the problems with these things is the compressor vibrations, it brake the contacts inside.
    I usually install them in the electric board.
    Chemi

  9. #9
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Klixon

    Hi Abe,

    The live and neutral connections on it are ONLY for a live and neutral connection.
    These connections are to power the transformer inside it.
    (hope you are not trying to put the control circuit through the L & N connections)


    The relay then provides a n/o and n/c contact. To which you can put 240v through it, up to 6A
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  10. #10
    Join Date
    Jun 2004
    Location
    Russia
    Age
    57
    Posts
    19
    Rep Power
    0

    Re: Klixon

    Hi,

    first of all - klixon is thermorelay. If temperature is too high, kontakts of klixon are off (or on) and ...

    The Kriwan needs thermistor - it is resistor with resistanse as function of temperature.

    You have to choose another Kriwan!

    BR

    Andrew

  11. #11
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Klixon

    Quote Originally Posted by chillin out
    Hi Abe,

    The live and neutral connections on it are ONLY for a live and neutral connection.
    These connections are to power the transformer inside it.
    (hope you are not trying to put the control circuit through the L & N connections)


    The relay then provides a n/o and n/c contact. To which you can put 240v through it, up to 6A

    I understand much much better now.......
    I know now.........the live and neutral powers the transformer.

    And I can use the relay to switch on and off........
    Its coming together now......

Similar Threads

  1. Compressor shutting down on overtemp?
    By Larry2 in forum Air Conditioning
    Replies: 50
    Last Post: 01-08-2006, 11:36 PM
  2. Help Me !
    By FRIDGE in forum Technical Discussions
    Replies: 17
    Last Post: 17-11-2004, 08:41 PM
  3. scroll compressors
    By bernard in forum Supermarket Refrigeration
    Replies: 16
    Last Post: 16-09-2004, 08:31 PM
  4. Evap motor no come on
    By Apprentice in forum Technical Discussions
    Replies: 13
    Last Post: 04-12-2003, 04:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •