Daikin rzq100 fault code L1...Help!
Hello all, i was sent to replace a main outdoor PCB on a daikin rzq100 today. The problem was that it was diagnosed by an ex employee of my company, so i probably should have looked into it a little more before i started.
Anyway i replaced the pcb and started the unit up....The breaker tripped at the distribution board. From previous experience i've had locked compressors trip breakers so i disconnected the compressor and ran the unit up again, 20mins past with no problems. so to make sure i ran the unit up once more with the compressor connected. 5mins passed then a loud BANG came from the outdoor unit and the breaker had tripped once again
Next time i ran the unit up i was greeted with an L1 fault code.
I can't find much info on this fault code.
Has anyone had any experience with this fault code?
Any advice? its all appriciated!
-
12-04-2011, 08:51 PM #2
Re: Daikin rzq100 fault code L1...Help!
megger the compressor to earth to check insulation is over 1 meg,check inverter pcb
Detect malfunctions by current value during waveform output before compressor startup.
Detect malfunctions by current sensor value during synchronized operation at the time of
startup.
Detect malfunctions using an MP-PAM series capacitor overvoltage sensor.
Malfunction
Decision
Conditions
When over-current is detected at the time of waveform output before operating the
compressor
When the current sensor malfunctions during synchronized operation
When overvoltage occurs in MP-PAM
In case of IGBT malfunction
In case of faulty jumper setting
Supposed
Causes
Faulty outdoor PC board (A1P)
•
IPM failure
•
Current sensor failure
•
MP-PAM failure
•
Failure of IGBT or drive circuit