25-02-2011, 06:04 PM #1
Check these driers out-and the pebble, white metal and copper
There bleedin awful, Any comments??
26-02-2011, 02:37 PM #2
Re: Check these driers out-and the pebble, white metal and copper
Better in the drier than trying to go though the compressor. You should also find some cement dust there as well.......
27-02-2011, 11:59 AM #3
I wouldn't be to concerned with the debris (although not ideal) .Thats what driers are for .At a guess i'd say whoever assembled the drier assembly at last changing placed it on the ground prior to refitting it , where it picked up the crap.
The shards could be from poor manufacturing standards ,or a sign of things to come !
I would however be concerned with the discolouration .Either someone has been carrying out weld repairs and not using Nitro and/or the system has suffered a massive burnout at some stage.
The oil must be like treacle !
StuLast edited by stufus; 27-02-2011 at 12:05 PM.
Tool's ? check ! Condom's ? check !
11-03-2011, 07:05 AM #4
if clog happened at capillary pipe, there is possible come from molecularsive in drier?
and how about spec minimum viscosity for POE luricant?
11-03-2011, 08:04 AM #5
if you flush (in a closed circuit) that system, you can get rid of all the debris, decomponed oil, and anything you have there.
We once cleaned cement from a circuit in the Canary Islands. A sac of it was dropped into a 10" copper tube. Flushed with R22, and got it all. This R22 was later reused, not released.
Regards,
Nando.
Metal gaskets
By norseman in forum FundamentalsReplies: 1Last Post: 20-10-2010, 09:17 AM -
What do Additional Bi-Metal Sensors Do
By kubcat in forum DomesticReplies: 4Last Post: 09-01-2010, 06:20 PM -
Metal Treatment
By Samarjit Sen in forum Technical DiscussionsReplies: 4Last Post: 16-08-2007, 02:38 PM -
metal soap?
By monkey spanners in forum RefrigerantsReplies: 0Last Post: 30-05-2007, 07:14 PM -
Metal Treatment with low temperature
By Samarjit Sen in forum Refrigeration BooksReplies: 0Last Post: 14-09-2006, 05:39 AM