    Thermoking SL 400E



    Hi All

    I am having a problem with a TK SL 400E SmartReefer2 bringing up fault code 11,
    which means :Unit Controlling on Alternate Sensor ,...Does anyone know what they mean





  2. #2
    Join Date
    Nov 2010
    Location
    The Netherlands
    Age
    64
    Posts
    134
    Rep Power
    14

    Re: Thermoking SL 400E

    Most likely is the return air sensor is defective and it's controlling on discharge temperature. I would imagine you also have code 03 (return) in there somewhere. Check on the display if the box temperature reading is correct.

  3. #3
    Join Date
    Oct 2010
    Location
    Spain
    Age
    57
    Posts
    31
    Rep Power
    0

    Re: Thermoking SL 400E

    you're right, the problem is that there are three failures 03,203 and 11,but one that is not erase its 11.
    anyway I'm a beginner so I think I'll start by changing all the sensors,
    Thank you very much for your advice

  4. #4
    Join Date
    Nov 2010
    Location
    The Netherlands
    Age
    64
    Posts
    134
    Rep Power
    14

    Re: Thermoking SL 400E

    Be careful changing a return sensor as they are graded. You will have to recalibrate the sensor in the maintenance menu

  5. #5
    Join Date
    Oct 2010
    Location
    Spain
    Age
    57
    Posts
    31
    Rep Power
    0

    Re: Thermoking SL 400E

    could you be a little more explicit,

  6. #6
    Join Date
    Oct 2010
    Location
    Spain
    Age
    57
    Posts
    31
    Rep Power
    0

    Re: Thermoking SL 400E

    is a complicated procedure? problem is that this equipment is not worked well for a long time, many "experts" have tried to fix it, The return sensors might not even be good, because I found removed from the circuit

  7. #7
    Join Date
    Mar 2009
    Location
    Brisbane, Australia
    Age
    65
    Posts
    197
    Rep Power
    16

    Re: Thermoking SL 400E

    G'day demicv;

    I think what Robert's trying to say, is that the sensor has a reference code on it (eg; 5G, 2B - something like that.) This needs to be calibrated into the controller to ensure the correct operation of the unit. These units also have similar sensors which are not marked with such a code and as such they don't need to be calibrated but their functions are quite different, such as ambient temperature.

    You will need to refer to the green controller manual for instruction on the calibrating these sensors into the controller.

    Best regards...

  8. #8
    Join Date
    Oct 2010
    Location
    Spain
    Age
    57
    Posts
    31
    Rep Power
    0

    Re: Thermoking SL 400E

    can anyone help me to get into guarded access
    mode so I can recalibrate the return air sensor,its a SR2 processor


  9. #9
    Join Date
    Oct 2010
    Location
    Spain
    Age
    57
    Posts
    31
    Rep Power
    0

    Re: Thermoking SL 400E

    or if anyone has a service manual for TK SL 400E SR2

  10. #10
    Join Date
    Apr 2009
    Location
    n ireland
    Posts
    13
    Rep Power
    0

    Re: Thermoking SL 400E

    This unit will bring up these codes due to a difference between the two return air sensors. There is two sensors one for control and one for display. Check in the sensor menu for both return sensors. It will more than likely need alarm codes cleared.

  11. #11
    Join Date
    Nov 2010
    Location
    The Netherlands
    Age
    64
    Posts
    134
    Rep Power
    14

    Re: Thermoking SL 400E

    Sorry chaps been away in Germany for a couple of days.
    The TK graded sensors have a number and letter code eg, 6H or 4L. The numbers being 1-9 and the letters H, L or nothing (meaning High, Low or middle) Once in guarded access you can choose sensor calibration, the sensor to be calibrated and then adjust and set. To enter guarded access:
    Unit on not running
    Press menu and enter operaters menu
    Press the blank button and exit together to enter the maintenance menu
    Scroll to sensor calibrate and press select
    Scroll to the correct sensor and select
    Adjust to new sensor and accept.

  12. #12
    Join Date
    Oct 2010
    Location
    Spain
    Age
    57
    Posts
    31
    Rep Power
    0

    Re: Thermoking SL 400E

    Thanks a lot for the advices, I did everything you told me and it's working well.

  13. #13
    Join Date
    Mar 2009
    Location
    Brisbane, Australia
    Age
    65
    Posts
    197
    Rep Power
    16

    Re: Thermoking SL 400E

    What's your email address and I'll shoot over the service manual?
    Tony...

  14. #14
    Join Date
    Feb 2011
    Location
    lebanon
    Age
    51
    Posts
    5
    Rep Power
    0

    Re: Thermoking SL 400E

    hi you can sent me service manual for sl 400e please.
    my email: anashadaya@hotmail.com
    thank you.

Similar Threads

  1. Thermoking SL-400e Defrost de-icing problem
    By Seban in forum Transport
    Replies: 4
    Last Post: 07-10-2010, 08:25 AM
  2. md2 thermoking
    By tnk in forum Transport
    Replies: 3
    Last Post: 02-08-2010, 02:14 AM
  3. ThermoKing SB II
    By Yurij I in forum Transport
    Replies: 20
    Last Post: 12-02-2010, 08:18 PM
  4. thermoking sb3 -sb-sle
    By cooljack in forum Transport
    Replies: 4
    Last Post: 16-06-2009, 03:35 AM
  5. thermoking sb3 -sb-sle
    By cooljack in forum Electrical
    Replies: 1
    Last Post: 15-06-2009, 08:09 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •