08-02-2011, 03:48 PM #1
Thermoking SL 400E
Hi All
I am having a problem with a TK SL 400E SmartReefer2 bringing up fault code 11,
which means :Unit Controlling on Alternate Sensor ,...Does anyone know what they mean
-
08-02-2011, 06:16 PM #2
Re: Thermoking SL 400E
Most likely is the return air sensor is defective and it's controlling on discharge temperature. I would imagine you also have code 03 (return) in there somewhere. Check on the display if the box temperature reading is correct.
-
08-02-2011, 07:05 PM #3
Re: Thermoking SL 400E
you're right, the problem is that there are three failures 03,203 and 11,but one that is not erase its 11.
anyway I'm a beginner so I think I'll start by changing all the sensors,
Thank you very much for your advice
-
08-02-2011, 07:17 PM #4
Re: Thermoking SL 400E
Be careful changing a return sensor as they are graded. You will have to recalibrate the sensor in the maintenance menu
-
08-02-2011, 07:31 PM #5
Re: Thermoking SL 400E
could you be a little more explicit,
-
08-02-2011, 07:42 PM #6
Re: Thermoking SL 400E
is a complicated procedure? problem is that this equipment is not worked well for a long time, many "experts" have tried to fix it, The return sensors might not even be good, because I found removed from the circuit
-
09-02-2011, 05:58 AM #7
Re: Thermoking SL 400E
G'day demicv;
I think what Robert's trying to say, is that the sensor has a reference code on it (eg; 5G, 2B - something like that.) This needs to be calibrated into the controller to ensure the correct operation of the unit. These units also have similar sensors which are not marked with such a code and as such they don't need to be calibrated but their functions are quite different, such as ambient temperature.
You will need to refer to the green controller manual for instruction on the calibrating these sensors into the controller.
Best regards...
-
09-02-2011, 08:45 AM #8
Re: Thermoking SL 400E
can anyone help me to get into guarded access
mode so I can recalibrate the return air sensor,its a SR2 processor
-
09-02-2011, 08:48 AM #9
Re: Thermoking SL 400E
or if anyone has a service manual for TK SL 400E SR2
-
09-02-2011, 07:38 PM #10
Re: Thermoking SL 400E
This unit will bring up these codes due to a difference between the two return air sensors. There is two sensors one for control and one for display. Check in the sensor menu for both return sensors. It will more than likely need alarm codes cleared.
-
10-02-2011, 07:09 PM #11
Re: Thermoking SL 400E
Sorry chaps been away in Germany for a couple of days.
The TK graded sensors have a number and letter code eg, 6H or 4L. The numbers being 1-9 and the letters H, L or nothing (meaning High, Low or middle) Once in guarded access you can choose sensor calibration, the sensor to be calibrated and then adjust and set. To enter guarded access:
Unit on not running
Press menu and enter operaters menu
Press the blank button and exit together to enter the maintenance menu
Scroll to sensor calibrate and press select
Scroll to the correct sensor and select
Adjust to new sensor and accept.
-
10-02-2011, 09:04 PM #12
Re: Thermoking SL 400E
Thanks a lot for the advices, I did everything you told me and it's working well.
-
15-02-2011, 06:03 AM #13
Re: Thermoking SL 400E
What's your email address and I'll shoot over the service manual?
Tony...
-
16-02-2011, 11:03 PM #14
Re: Thermoking SL 400E
hi you can sent me service manual for sl 400e please.
my email: anashadaya@hotmail.com
thank you.
Similar Threads
-
Thermoking SL-400e Defrost de-icing problem
By Seban in forum TransportReplies: 4Last Post: 07-10-2010, 08:25 AM -
md2 thermoking
By tnk in forum TransportReplies: 3Last Post: 02-08-2010, 02:14 AM -
ThermoKing SB II
By Yurij I in forum TransportReplies: 20Last Post: 12-02-2010, 08:18 PM -
thermoking sb3 -sb-sle
By cooljack in forum TransportReplies: 4Last Post: 16-06-2009, 03:35 AM -
thermoking sb3 -sb-sle
By cooljack in forum ElectricalReplies: 1Last Post: 15-06-2009, 08:09 PM