    Data Aire with scroll's



    I worked on a thirty ton two circuit downflow air cooled Data Aire unit. The one circuit with a scroll compressor was tripping on the hpc. There was no rhyme or reason as to why or when it would trip. Cold outside,warm out etc. The discharge pipe came out three feet horizontal and fifty up the wall to the aircooled condenser. There was traps on the liquid line so liquid would not migrate back to the compressor, the crankcase heater was working. After checking all the common problems I decided to install a checkvalve on the outlet of the discharge line. That worked.

    I know scrolls have checkvalves in the compressors and usually when they go bad you can here the scroll spin backwards when the compressor shuts down but not in this case. This was a new install. So my question is why did this work?
    We have thirty other units piped the same way and no problems. Is it possible a check valve was never installed on this compressor and at start up it would trip. It never did it while I was there. The other circuit never tripped



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Data Aire with scroll's

    Anything is possible but most likely a duff NRV . Would the comp hold a pump-down before the new valve was fitted?
    If all is well now and stays that way , well spotted.
    Alternatively if you have the time and the comp has rotoloks swap it onto the other circuit to see what happens.
    Or sit back and pat yourself on the back for a job well done
    OH nearly forgot get onto the manufacturer and give them both barrels and an invoice for your time..
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Data Aire with scroll's

    a duff NRV
    Recently is happening more frequently than not. We had 12-14 compressors with broken scrolls by liquid return from the discharge.

  4. #4
    Join Date
    Jan 2007
    Location
    USA
    Age
    59
    Posts
    145
    Rep Power
    18

    Re: Data Aire with scroll's

    Thanks for the feedback.

Similar Threads

  1. McQuay centrifugal chiller data requirement!
    By karl2009 in forum Air Conditioning
    Replies: 7
    Last Post: 05-05-2011, 08:55 AM
  2. Multiple-input data logger
    By desA in forum New Technologies
    Replies: 3
    Last Post: 17-10-2010, 10:44 PM
  3. Data Center Cooling Estimator
    By josei in forum Refrigeration Books
    Replies: 2
    Last Post: 23-06-2010, 02:46 PM
  4. Container Data info
    By Paulajayne in forum Technical Discussions
    Replies: 7
    Last Post: 06-06-2007, 02:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •