Results 1 to 10 of 10
Thread: help please
26-01-2011, 08:58 AM #1
help please
Hi forum
I have just had a 20 kw invertor installed
but the guy has had trouble getting it working
he said he would come back thursday but
today is so damm hot
it is displaying a U3 error
I think this means it is not commissioned
how do I fix it?
jabela
26-01-2011, 09:03 AM #2
Re: help please
Hi jabela
It might help the members if you posted some details about your system, such as, Make, Model, Number of indoor units, Number of outdoor units, Refirgerant type etc.
From where we are, we cannot see your system.
26-01-2011, 09:26 AM #3
Re: help please
Thanks for the prompt response
it is a daikin
3 phase
invertor
ODU is RZYQ8PY1 (built 9/2010)
IDU FDYQ200PV1
just installed yesterday
U3 error keeps coming up
from my reading it may not have been commissioned?
i am not sure what this means
is there a process of comissioning
I can not find an operations manual
jabela
26-01-2011, 09:29 AM #4
Re: help please
addit
there are 11 outlets
on 2 zones
i gather i press the zone 1 and 2 till the green LED is displayed, and hence they are usable
jabela
26-01-2011, 03:45 PM #5
Re: help please
The U3 error means that the system has not been properly commissioned.
I would get the installer back to complete the job properly.
The are a number of settings/checks to do, in addition to adding any additional refrigerant, prior to carrying out the test operation.
The attached pdf explains how to carry out the test operation
26-01-2011, 11:31 PM #6
Re: help please
Beware of voiding your warranty by playing with a non-commissioned system.
It might prove expensive if things go wrong or you extend the commissioning time and the technician has to start again because of your actions.Brian - Newton Abbot, Devon, UK
27-01-2011, 03:31 AM #7
Re: help please
jabela,
I installed one of these last November and they take about an hour and a half to commission properly.Remember we are here for a good time, not a long time.
Trust me i'm a Fridgy.
27-01-2011, 10:51 AM #8
Re: help please
Thanks for the suggestions. A different guy came back today
And tinkered for a little while and commissioned the unit
He could not understand why the first guy could not complete the job
All worked well for about 2 hrs
Then it stopped working
And started to display the error code LC
Anyhow. The guy is coming back
Again tomorrow.
What does it all mean.
Jabela
Thanks for the responses
28-01-2011, 12:31 PM #9
Re: help please
Hey all
Another guy came back today
And fixed the problem
The problem was that one of the 3 phases had a dodgy connection
It was intermittently connecting and disconnecting
The guy today found the wire responsible and secured it
And took some photos to stir up his mate about a dodgy install
The guy explained that without the 3 phase working the unit could not go through commissioning, and hence the u3 error. The yesterday must have been lucky enough to be able to commission the unit while there was a temporary connection. Then after a while the 3rd phase was lost and hence it became a LC error.
Anyhow.
With the wire secured, all is perfect.
Thanks all for your (collective) help
Jabela
28-01-2011, 06:50 PM #10
Re: help please
I took a leaf out of this guys book. Last year I was working with and Airedale tech who was comissioning 2 close control units I'd installed.
First thing he did was check every terminal was tight in the electric panel.
No loose wires but later found that the pressure sensors connected @rse about face on the terminal block.