Results 1 to 6 of 6
Thread: Compressor for island case
-
09-08-2005, 08:56 AM #1
Compressor for island case
Hello experts,
I need make island case with built-in condensig unit and capillary tube.
The air temperature inside may vary from minus 6 C to plus 6 C.
Should I use LBP or MBP Embraco compressor for condensig unit ?
Which must be evaporation temperature?
Thanks for any advice
-
09-08-2005, 11:01 PM #2
Re: Compressor for island case
Tralex , i didn't understand what you want to build . . . please explain
Engineering, sciences, math, physics and my brain will generate "not responding " soon
-
10-08-2005, 11:09 AM #3
Re: Compressor for island case
Hello botrous,
I'm sorry for my inefficiency to explain what I want.
Now I drew my question.
Thank you
-
10-08-2005, 01:09 PM #4
Re: Compressor for island case
You need MBP or LBP assuming you want to evaporate around -16C
to achieve -6C
You need to check Embraco table for that compressor to see if it can achieve the required duty at that evap temp
-
10-08-2005, 06:49 PM #5
Re: Compressor for island case
I agree with Ayub . . . send an email to the Embarco and they can help you select the right compressor for your application or see the Embarco tables
Engineering, sciences, math, physics and my brain will generate "not responding " soon
-
14-08-2005, 12:08 PM #6
Re: Compressor for island case
You also need to check the condenser size if you intend using the existing one. The safest would be to use a standard condensing unit sized to the (new) capacity of the existing evap. Remember the evap will give slighlty more capacity at the high temperature (depending on the delta T of course).