    Trane CGCE207 Problems



    Trane CGCE207 Chillers

    Having some problems with the above model.
    1. Unit trips on h/p when first run, seems to settle after several re-starts.
    2. Unit trips out on 'antifreeze', does anyone know the antifreeze seting and if/how these can be adjusted?

    We have 2 units duty/standby running approx at 2degC flow and about 6degC return, 15% glycol.

    Also anyone know wher i can get a service manual for the above?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Trane CGCE207 Problems

    Hi AW, welcome to the forum.

    Which part of the world are you in ?, you profile doesn't list your location.

    Tranes' website search facility is off-line at the moment so am not sure what they have available on that chiller.

    Perhaps you could try there yourself, if you haven't already done so.

    http://www.trane.com
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: Trane CGCE207 Problems

    Welcome AW.

    If there's nothing on the web, try your local Trane office. They can almost certainly provide you with a manual, although they may well charge an admin. fee, specially for older units. In the U.K. they used to charge £50 a manual - not sure what it is now.
    If you're in the U.K, I'd suggest ringing their Service technical support. It's free & they're usually pretty helpful, unless they think you're a chancer or dangerously un-knowlegable about what you're doing. Not that I'm suggesting you are, you understand.
    IIRC (years since I worked on one), this model had an antifreeze thermostat. If the wiring diagram is still in the machine, you should be able to see from the key which 'bit' it is. And then the items themselves are labelled with the same reference as in the key, unless someone's replaced them in the past, of course. The 'stat just had an adjustment knob on it. As to what you should set the 'stat to, I don't know the answer with glycol in the system. I'd imagine set it for 3 or 4 degreees below your water temp. set point, but I'm sure one of the others here can give you a better answer.
    Bear in mind that the 'stat may be faulty or there may be a wiring fault and that's why it's cutting out.
    As for the H.P. trip, there's a lot of things that can cause it. The ambient air temp. could be very high, the condenser could be choked with dust & dirt, or even a high water temp. can cause it on those machines.

  4. #4
    Join Date
    Aug 2011
    Location
    Bulgaria
    Age
    46
    Posts
    8
    Rep Power
    0

    Re: Trane CGCE207 Problems

    Hello,dear.I have problem with this chiller.Bad colege is set off side"B".I select position "B" ,work side "A".
    I select side "A" work A.I select side"A+B" work only "A".May be he blocked with jumpers.HELP me please.
    Thanks.

  5. #5
    Join Date
    Oct 2010
    Location
    Greece
    Age
    52
    Posts
    97
    Rep Power
    14

    Re: Trane CGCE207 Problems

    Hi AWCarillion and Tanov,
    I suppose that your chiller has 4 scroll compressors running with R22 and have SCM controller with 2 circuits.
    About selector switch most probably the controller had E2PROM failure (HARD 4 (HRD4)). You have to reprogram it.
    About antifreeze please check integrity of water sensor.
    About HP please check also that your HP switch is well operating.
    Also this unit must have a two speed centrifugal fan. Check its operation.
    I have send you both the service manual of SCM but I had a delivery failure for AWCarillion. Please check your account.
    Usually these units have 5°C differential temperature at 7°C water outlet with no glycol in the system and about 5°C approach.
    In 2°C water outlet and 15% glycol in the system the approach should be something between 5,5°C and 6°C.
    If you have a dead band +- 1,5 means that the unit will stop at 0,5°C – 6°approach = -5,5°C saturated temperature in evaporator.
    If you have ethylene glycol 15% means -5,8°C freeze point. If you have propylene glycol 15% means -4,9°C.
    You can understand that you are crossing the line of safe operation.
    If you have ethylene glycol I suggest you to have 22% (Freeze point -9,6°C) and if you have propylene glycol I suggest you to have 25% (Freeze point -9,6°C)
    Regards,
    CV

  6. #6
    Join Date
    Oct 2010
    Location
    Greece
    Age
    52
    Posts
    97
    Rep Power
    14

    Re: Trane CGCE207 Problems

    Sorry, I didn’t see the original post date!!!

  7. #7
    Join Date
    Aug 2011
    Location
    Bulgaria
    Age
    46
    Posts
    8
    Rep Power
    0

    Re: Trane CGCE207 Problems

    how I can programming it most easy

  8. #8
    Join Date
    Aug 2011
    Location
    Bulgaria
    Age
    46
    Posts
    8
    Rep Power
    0

    Re: Trane CGCE207 Problems

    with programmer for eeprom or with program key?
    Have there two chip eeprom same?

  9. #9
    Join Date
    Aug 2011
    Location
    Bulgaria
    Age
    46
    Posts
    8
    Rep Power
    0

    Re: Trane CGCE207 Problems

    From where I an download dump ?

  10. #10
    Join Date
    Oct 2010
    Location
    Greece
    Age
    52
    Posts
    97
    Rep Power
    14

    Re: Trane CGCE207 Problems

    Hi,
    Please check your email. I have send you the programming guide.
    Regards,
    CV

  11. #11
    Join Date
    Aug 2011
    Location
    Bulgaria
    Age
    46
    Posts
    8
    Rep Power
    0

    Re: Trane CGCE207 Problems

    please try again CLIMA@MAIL.BG.
    I can not receive.

  12. #12
    Join Date
    Oct 2010
    Location
    Greece
    Age
    52
    Posts
    97
    Rep Power
    14

    Re: Trane CGCE207 Problems

    Mail send.
    CV

  13. #13
    Join Date
    Aug 2011
    Location
    Bulgaria
    Age
    46
    Posts
    8
    Rep Power
    0

    Re: Trane CGCE207 Problems

    Perfect.you are the best.thank you very much.you decided very important problem.

Similar Threads

  1. Trane RTAD125 Problems
    By Latte in forum Trouble Shooting
    Replies: 10
    Last Post: 10-05-2010, 11:38 AM
  2. Replies: 10
    Last Post: 18-03-2006, 07:35 PM
  3. Oil return problems
    By Peter_1 in forum Industrial
    Replies: 37
    Last Post: 23-08-2004, 11:30 PM
  4. oil pressure problems on air dryer
    By edge in forum Trouble Shooting
    Replies: 1
    Last Post: 16-07-2002, 02:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •