SuperHeat Setting
Hi All,
Got a bit of a debate going here about setting superheats.
Case:
Evaporator temperature (converted from pressure)
-24 Celsius
Temperature at the bulb -20
Is that a correct way to set 4K superheat or should the temperature at the bulb be -28??
-
23-12-2010, 10:27 PM #2
Re: SuperHeat Setting
Hi Bojan.
go to www.kueba.de and look for the service tools area.
-
23-12-2010, 11:04 PM #3
Re: SuperHeat Setting
Found this on the sporlan/parker site
http://www.parker.com/literature/Spo...nous/Form1.pdf
Basically if you are evaporating at -4C for example which you have determined by taking the pressure at the evaporator outlet and converting that pressure into temperature with a pt chart, you then take the temperature at the outlet and compare the two, say its 3C then you have 7K superheat. Its K for Kelvin as its a difference in temperature and not an actual temperature.
JonLast edited by monkey spanners; 23-12-2010 at 11:04 PM. Reason: must type quicker!!!!!!
-
24-12-2010, 08:15 AM #4
Re: SuperHeat Setting
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
TEV superheat setting and low temperatures
By DaBit in forum FundamentalsReplies: 11Last Post: 01-03-2010, 02:11 AM -
setting superheat
By sidi in forum Air ConditioningReplies: 6Last Post: 20-05-2008, 05:06 AM -
setting up a unit using superheat
By marc5180 in forum Trouble ShootingReplies: 5Last Post: 26-06-2007, 11:25 AM -
Setting superheat settings
By Abe in forum CommercialReplies: 12Last Post: 10-06-2004, 02:20 PM