    Ice on the liquid line filter



    Hi

    After installing a new ar conditioning SPLIT, there is ice on the liquid line filter. What can it be ?

    Moisés



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Ice on the liquid line filter

    Is it only on the filter?

    Where abouts is the filter installed?

    Is it a seperate filter that you have installed or is it part of the outdoor unit?

  3. #3
    Join Date
    Dec 2008
    Location
    Brazil
    Posts
    106
    Rep Power
    16

    Re: Ice on the liquid line filter

    Sorry the guy gave me wrong information.
    According to him It's the liquid line valve that is frozen and the pressure is 56psi and 7ºc
    Moises

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Ice on the liquid line filter

    Frozen at 7C??

    Doesn't make any sense.

  5. #5
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: Ice on the liquid line filter

    The liquid line valve from the receiver?

    Is the valve fully open and is there a column of liquid in the sight glass?

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Ice on the liquid line filter

    Most splits now-a-days do not have a liquid line as such.

    Expansion is done mainly within the outdoor unit and continues along the line set.

    What are the ambient conditions ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: Ice on the liquid line filter

    I thought the expansion started at the evaporator (indoor unit) via the TXV, and along the suction line

    Are you refering to a back to back/package unit?

    I had a similar problem once when pumping a system down. The TXV needle valve was set to have a bleed/equalising position, and the service valve on the liquid line from the receiver wasn't closed tight enough due to it being seized. The resulting effect was the compressor sucking a partial vacuum in the evaporator, and partially through the liquid line via the bleed effect of the TXV. Then in turn the liquid from the receiver expanding through the faulty service valve, and causing partial frosting of the service valve and sweating of the suction line.

    Maybe the same here, either that or they might have a small leak on the liquid line connection to the receiver.

  8. #8
    Join Date
    Aug 2008
    Location
    ireland
    Posts
    75
    Rep Power
    16

    Re: Ice on the liquid line filter

    Expansion is done in the outside unit, so Brian is right, no liquid line as such, in standard ac split systems. I think the Japanese started this, to dodge the subcooled liquid problem, amongst other things. Sorry , a bit off topic.

  9. #9
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: Ice on the liquid line filter


    Please don't take this the wrong way.

    But I'm confused and worried now, is there a new type of refrigeration system that works with a different principle, that I've missed out on? Please enlighten me if I have missed out on it.

    If expansion of the liquid takes place inside a condensing unit, then surely the split is in heating mode and the condensor is now an evaporator. The system mentioned is just an aircon split, no mention of a heat pump.

    If it was expanding in the cooling mode, then surely the liquid would be starting to boil off in the condensor coil, and the pressures would be way off scale. And you would never get rid off the bubbles in the sight glass.

    This would be similar to being short of refrigerant, plus any pressure control would be tripping out all of the time. And there would be a constant hiss at the TXV due to gas passing through it, and not enough liquid.

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Ice on the liquid line filter

    Few single splits have TXVs in them, they use cap lines.

    Check a few line diagrams.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: Ice on the liquid line filter

    Quote Originally Posted by chilliwilly View Post

    Please don't take this the wrong way.

    But I'm confused and worried now, is there a new type of refrigeration system that works with a different principle, that I've missed out on? Please enlighten me if I have missed out on it.

    If expansion of the liquid takes place inside a condensing unit, then surely the split is in heating mode and the condensor is now an evaporator. The system mentioned is just an aircon split, no mention of a heat pump.

    If it was expanding in the cooling mode, then surely the liquid would be starting to boil off in the condensor coil, and the pressures would be way off scale. And you would never get rid off the bubbles in the sight glass.

    This would be similar to being short of refrigerant, plus any pressure control would be tripping out all of the time. And there would be a constant hiss at the TXV due to gas passing through it, and not enough liquid.
    Cap tube or exv is in the outdoor unit the small pipe is effectivly part of the evaporator or an expansion line if you like, thats why in modern splits both pipes are insulated.
    No drier is fitted in the field or sightglass for that matter. These systems are critically charged like a domestic fridge.

    Jon

  12. #12
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: Ice on the liquid line filter

    You live and learn, I have missed out on a new method of piping up a line set. Its been over five years since I fit a split. And they were second hand two year old Mits units charged with 410a, and had TXVs in the AHU.

    I knew you insulated both lines for heat pumps for obvious reasons, so whenever Ive looked up at any line sets any where I just assumed they were heat pump configured. Assumption in this case being the mother of kcufup!

    Question.

    If the splits are critically charged and have cap feeders, won't they have limited cooling capacity and have cooling problems regarding environmental conditons and varying heat load?

    If not TXVs then I'll assume their AEVs? otherwise how would you adjust the superheat setting from outside?

  13. #13
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: Ice on the liquid line filter

    Most splits have one capiliary in the outdoor unit which partly expands the refrigerant and aslo one in the indoor unit which completes the expansion process...i would say the cause of ice is gas shortage but no idea why he say he has a drier icing up,never see a drier on a wall split.

  14. #14
    Join Date
    Dec 2007
    Location
    uk
    Posts
    73
    Rep Power
    17

    Re: Ice on the liquid line filter

    Sounds like refrigerant shortage.
    ( some systems get a slight frost on the condensing unit liquid line valve, when first ran/commissioned, until pressures balance out)
    Is it pre charged? Is the charge correct for the pipe run?

  15. #15
    Join Date
    Dec 2010
    Location
    Fl,United States
    Posts
    16
    Rep Power
    0

    Re: Ice on the liquid line filter

    it can be a restriction but most likely a refrigerant issue under/overcharge....

  16. #16
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Ice on the liquid line filter

    Quote Originally Posted by DC5-T View Post
    it can be a restriction but most likely a refrigerant issue under/overcharge....
    How would an overcharged system lead to icing on the drier at +7C?

  17. #17
    joshuatan's Avatar
    joshuatan Guest

    Re: Ice on the liquid line filter

    In Malaysia you can commonly find manufacturers use capillary tube installed after the condensors in the outdoor unit. You can open the outdoor unit and see if there is a coil of capillary tubings just before the 'liquid' service valve. The piping will be cold as well so you will find both to be cold instead of 1 warm and 1 cold as usually found in units with txv's fitted.
    I have checked that the pressure is normally around 100 psig and you should not have a filter drier fitted!!
    Both pipes also need to be insulated. Please note that it is used extensively from about the range of 8000 to 22000 btu/hr. cooling capacity units

Similar Threads

  1. SullAir/Jordan Valve
    By jaysephus in forum Industrial Compressors
    Replies: 42
    Last Post: 12-01-2010, 04:29 AM
  2. Question about liquid line sizing
    By kengineering in forum Technical Discussions
    Replies: 17
    Last Post: 22-07-2009, 01:48 AM
  3. one for the experrts (liquid line condensing)
    By frostedflake in forum Trouble Shooting
    Replies: 4
    Last Post: 11-02-2009, 04:48 PM
  4. liquid return through suction line after hot gas defrost period
    By coldkeeper1 in forum Supermarket Refrigeration
    Replies: 2
    Last Post: 19-06-2008, 10:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •