Daikin Magnetic Contactor
Hi all,
Just been to a job today where an electrician had been called out to find out why the house kept tripping out the main power breaker. Anyway he traced the problem to the Aircon unit. Instead of turning the breaker off to the unit. He cleaned out the dead rats inside the outdoor and tried to turn it on. It tripped the house again . So I was called to the house??
So I am told that a dead rat was laying across the magnetic contactor?? So after re wiring all the breakers and switches that the sparky disconnected I managed to turn the unit on....... BANG blue sparks fly from the magnetic contactor house trips .
Unit is a Daikin RY160LUY1 and I was wondering if anyone would know if any other damage could have been done prior to me turning it on? Before I turned it on I did notice some over heated cables. Just wondering if the rat could have burnt out the compressor at all. Its obvious the contactor is fried so I have a new one on order. Any other parts I should have ordered? Thanks for reading my long post.
-
13-12-2010, 03:48 PM #2
Re: Daikin Magnetic Contactor
Dont you just love rats..
Had this happen a few years back and the rats had chewed through cables etc etc.
You will need to check all wires to make sure they are ok.A little giveaway sign is if yhere are any dead one hanging from cables
Oh and put your gloves on and try and cover the holes were there getting in..
Regards
-
13-12-2010, 07:58 PM #3
Re: Daikin Magnetic Contactor
I would check all wiring pal. Mains, comms and thermistors those pissing rats will chew few anything.
Definatley check all your mains wiring to earth before you switch the unit on again.
Good luck
-
13-12-2010, 09:54 PM #4
-
14-12-2010, 08:12 PM #5
Re: Daikin Magnetic Contactor
Hi Jaceace I worked on a daikin vrv recently and found a 3 phase contactor had malfuctioned and caused a dead short this took out the M.C.B protecting the circuit and the fault current damaged/blew a p.c.b on outdoor unit. So I would check all the components on the outdoor unit. Also I would recommend and Insulation resistance test on the supply cables.
-
21-12-2010, 12:20 AM #6
Re: Daikin Magnetic Contactor
Hi all, This just seems to be getting worse. I checked all the cables on the outdoor unit before turning it back on after replacing the contactor. I then found the lcd controller did not come on. I went into the roof to find (3) f....ing mice fried in the indoor box. So I have power running to the box. I have 0volts coming out the transformer and no activity on the indoor pcb board. I think all the boards have been fried and will need replacing along with the transformer. I can not believe 5 mice total stuffed this guys aircon.
Similar Threads
-
Daikin not working... many problems
By stankovicv in forum Air ConditioningReplies: 26Last Post: 11-12-2010, 09:01 AM -
Contactor Bouncing or Hammering
By charlie dart in forum FundamentalsReplies: 6Last Post: 25-09-2010, 06:05 PM -
Mitsi City Multi VS Daikin VRV
By sumsor in forum FundamentalsReplies: 5Last Post: 14-07-2010, 05:54 PM -
Daikin AC parts from UK
By skel00 in forum Air ConditioningReplies: 5Last Post: 05-04-2009, 01:24 PM -
Fixing Daikin A3 Error
By Stuffy in forum Air ConditioningReplies: 3Last Post: 27-03-2009, 06:02 AM