    Daikin Magnetic Contactor



    Hi all,

    Just been to a job today where an electrician had been called out to find out why the house kept tripping out the main power breaker. Anyway he traced the problem to the Aircon unit. Instead of turning the breaker off to the unit. He cleaned out the dead rats inside the outdoor and tried to turn it on. It tripped the house again . So I was called to the house??

    So I am told that a dead rat was laying across the magnetic contactor?? So after re wiring all the breakers and switches that the sparky disconnected I managed to turn the unit on....... BANG blue sparks fly from the magnetic contactor house trips .

    Unit is a Daikin RY160LUY1 and I was wondering if anyone would know if any other damage could have been done prior to me turning it on? Before I turned it on I did notice some over heated cables. Just wondering if the rat could have burnt out the compressor at all. Its obvious the contactor is fried so I have a new one on order. Any other parts I should have ordered? Thanks for reading my long post.



  2. #2
    Join Date
    Aug 2009
    Location
    east anglia
    Age
    49
    Posts
    95
    Rep Power
    15

    Re: Daikin Magnetic Contactor

    Dont you just love rats..
    Had this happen a few years back and the rats had chewed through cables etc etc.
    You will need to check all wires to make sure they are ok.A little giveaway sign is if yhere are any dead one hanging from cables
    Oh and put your gloves on and try and cover the holes were there getting in..
    Regards

  3. #3
    Join Date
    Oct 2010
    Location
    flitwick
    Age
    40
    Posts
    12
    Rep Power
    0

    Re: Daikin Magnetic Contactor

    I would check all wiring pal. Mains, comms and thermistors those pissing rats will chew few anything.

    Definatley check all your mains wiring to earth before you switch the unit on again.

    Good luck

  4. #4
    Join Date
    Jul 2009
    Location
    Australia
    Posts
    32
    Rep Power
    0

    Re: Daikin Magnetic Contactor

    Quote Originally Posted by croc1774 View Post
    Dont you just love rats..
    Had this happen a few years back and the rats had chewed through cables etc etc.
    You will need to check all wires to make sure they are ok.A little giveaway sign is if yhere are any dead one hanging from cables
    Oh and put your gloves on and try and cover the holes were there getting in..
    Regards

    Hi thanks for your post,

    Yeah I was going to buy some mesh and cover the holes, Daikin just called and have sent the contactor. I must say they are a very helpful company and very efficient.

  5. #5
    Join Date
    Dec 2009
    Location
    England
    Age
    41
    Posts
    29
    Rep Power
    0

    Re: Daikin Magnetic Contactor

    Hi Jaceace I worked on a daikin vrv recently and found a 3 phase contactor had malfuctioned and caused a dead short this took out the M.C.B protecting the circuit and the fault current damaged/blew a p.c.b on outdoor unit. So I would check all the components on the outdoor unit. Also I would recommend and Insulation resistance test on the supply cables.

  6. #6
    Join Date
    Jul 2009
    Location
    Australia
    Posts
    32
    Rep Power
    0

    Re: Daikin Magnetic Contactor

    Hi all, This just seems to be getting worse. I checked all the cables on the outdoor unit before turning it back on after replacing the contactor. I then found the lcd controller did not come on. I went into the roof to find (3) f....ing mice fried in the indoor box. So I have power running to the box. I have 0volts coming out the transformer and no activity on the indoor pcb board. I think all the boards have been fried and will need replacing along with the transformer. I can not believe 5 mice total stuffed this guys aircon.

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Contactor Bouncing or Hammering
    By charlie dart in forum Fundamentals
    Replies: 6
    Last Post: 25-09-2010, 06:05 PM
  3. Mitsi City Multi VS Daikin VRV
    By sumsor in forum Fundamentals
    Replies: 5
    Last Post: 14-07-2010, 05:54 PM
  4. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  5. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •