Results 1 to 2 of 2
    Sep 2009
    libya
    41
    35
    Type of Compressors
    Good day everybody,
    Could you tell me what is the difference between single stage compressor and booster?
    Thanks & Regards
    Nov 2010
    London
    624
    15
    Re: Type of Compressors
    A booster is simply the low stage compressor of a two stage system.
    Usually also requires an oil pump when the boost is a screw compressor.
    If the overall compression ratio is 9/1 then the boost will handle as near as possible the square root of the overall compression ratio which would be 3/1 leaving the high stage compressor also to handle a ratio of 3/1. The actual ratios selected by the designers depends more on the required mid and lower saturated evaporating temperatures intended.
    But when the absolute suction and discharge pressures are 1 and 9 the boost will have a pressure across it to deliver oil of just 3 bar whereas the high stage will have a pressure drop across it of 6 bar enough to preclude the need for an oil pump.
    Sorry - I tried to upload a graphic of the typical pipe circuitry and component layout but the image uploader stalls.
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.