Results 1 to 9 of 9
    Jan 2009
    Scotland
    79
    Cold weather delights!
    Hello all,
    This may seem like a silly question.....
    Been at a couple of cold rooms today which are suffering from the cold. Condensing units outside with no fan speed controller fitted so unit ends up tripping on lp switch.
    When the units were started back up again i noticed that the site glasses were bubbling.
    Can the extreme cold (it was -22.4 celcius here the other morning ) cause the bubbles in the glass or am I barking up the wrong tree?
    Thanks in advance
    Sep 2003
    ISRAEL
    72
    4,248
    Re: Cold weather delights!
    You need head pressure controll also on the first fan.
    And yes, its the low temp that causes the bubbles.
    Jan 2009
    Scotland
    79
    Cheers Chemi, I take it that its due to the high side pressure being dropped to such a low level. What is the actual reason that there is not a solid stream of liquid?
    Jun 2010
    Yorkshire
    59
    520
    Did the bubbles clear or did they persist?
    Aug 2009
    New Zealand
    2,554
    26
    Quote Originally Posted by G Cook View Post
    A number or reasons.
    You do not have the correct mass flow of refrigerant (hence tripping on LP)
    Some of the refrigerant is held up in the condensor (no all flowing) balancing heat transfer
    Jan 2009
    Scotland
    79
    The bubbles persisted chilly.
    Nov 2009
    Western PA
    48
    69
    15
    http://www.sporlanonline.com/90-30.htm
    http://www.sporlanonline.com/90-31.htm
    http://www.sporlanonline.com/90-30-1.htm
    These are the guidelines that i follow for charging units that will see temperature extremes.
    Feb 2009
    telford
    2,092
    33
    tell me about the cold got 2 vans with gah units fitted ,they are heat/cool units trying to maintain +16 celcius and they cannot do it arghhhh
    Dec 2004
    U.K
    55
    518
    21
    Quote Originally Posted by cadwaladr View Post
    They will struggle in low ambients, have they got heater pads in the drain pans? If they have perhaps you could add a relay to energise them in heat mode which will add a bit more?
  1. Is there any kits to make A/c hotter in cold weather
    By Chris2005 in forum Air Conditioning
    Last Post: 13-07-2009, 03:40 AM
  2. Cold weather charging
    By FEISTY in forum Tools and Calculators
    Last Post: 27-02-2009, 08:14 AM
  3. Breakdowns in cold weather
    By back2space in forum Air Conditioning
    Last Post: 10-12-2008, 01:19 AM
  4. Cold Weather and Maintenance Visits!
    By Grizzly in forum Chit Chat & Service Stories
    Last Post: 15-12-2007, 10:26 AM