    Daikin vrv u4 problem



    Sir any one can help me find a solution,im havin a problem on u4 error( transmission wiring between indoor and outdoor unit)i have already check the wires but error still persist...unit installed with two evaporator in one condenser, but we took the one evaporator board to install to the other unit mean only one unit now is connected to the condenser,we have re-connected the F1 and F2 from the remaining unit properly but U4 code still persist...can you help me or redirect me to the right thread in this forum?tnx



  2. #2
    Join Date
    Aug 2009
    Location
    Singapore
    Age
    47
    Posts
    42
    Rep Power
    0

    Re: Daikin vrv u4 problem

    Try to reset the unit..

  3. #3
    Join Date
    Sep 2010
    Location
    England
    Posts
    40
    Rep Power
    0

    Re: Daikin vrv u4 problem

    Model numbers??

  4. #4
    Join Date
    Mar 2009
    Location
    UK
    Posts
    17
    Rep Power
    0

    Re: Daikin vrv u4 problem

    Units will need to be correctly addressed; the outdoor unit is probably looking for the unit you have removed. Also be aware , running for long periods at low load can be fatal to the outdoor unit .

  5. #5
    jay2's Avatar
    jay2 Guest

    Re: Daikin vrv u4 problem

    Quote Originally Posted by wozza View Post
    Model numbers??
    Model: RSX8KTAL

    tnx sir

  6. #6
    jay2's Avatar
    jay2 Guest

    Re: Daikin vrv u4 problem

    Quote Originally Posted by ksm View Post
    Try to reset the unit..
    Ive tried sir both indoor and outdoor..but still persist,i was wondering maybe there are some resetting from the outdoor unit to detect that only 1 evaporator is running instead of two...

  7. #7
    jay2's Avatar
    jay2 Guest

    Re: Daikin vrv u4 problem

    Quote Originally Posted by Dr Death View Post
    Units will need to be correctly addressed; the outdoor unit is probably looking for the unit you have removed. Also be aware , running for long periods at low load can be fatal to the outdoor unit .
    yes sir I was thinking of resetting the address,but the problem is this is my first time to encounter this model,we are not the one who installed the unit....can you send me instructions?tnx

  8. #8
    Join Date
    Aug 2008
    Location
    London
    Age
    42
    Posts
    55
    Rep Power
    16

    Re: Daikin vrv u4 problem

    I dont suppose you could offer some advise or help on a problem i have been asked about? im more chiller biased and dont really get involved with the VRV/splits unless necessary..

    1 x REYQ 12M7W1B LINKED TO

    1 X REYQ 10M7W1B

    13 X CASSETTE INDOORS AT HIGH LEVEL

    7 X LOCAL CONTROLLERS

    1 X DCS302 CENTRAL CONTROLLER

    1 X DST301 SCHEDULE TIMER

    THE WHOLE SYSTEM SHUTS DOWN AT INTERMITTENT TIMES ON U4 FAULT CODE

    THEY FEEL THE CENTRAL CONTROLLER IS FIGHTING THE LOCAL CONTROL BUT CANT BE SURE

    THEY RESET 1 LOCAL CONTROLLER TO CLEAR FAULT CODES THE WHOLE SYSTEM SHUTS DOWN

    SOMETIMES LASTS 4 HOUR OR 4 DAYS NO RHYME OR REASON BUT I NEED TO GET IT SORTED ASAP

    Any idea??

    many thanks

    Wilko

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. problem with DAIKIN FCQ 71 > i need technical book
    By mimifrigo in forum Air Conditioning
    Replies: 7
    Last Post: 13-01-2010, 03:06 PM
  3. DAIKIN problem
    By mimifrigo in forum Air Conditioning
    Replies: 3
    Last Post: 05-01-2010, 09:02 PM
  4. Samsung Vivace Problem AQV24VBCN
    By goldpau in forum Air Conditioning
    Replies: 0
    Last Post: 18-09-2009, 06:28 PM
  5. Saunier Duval Problem
    By mallorcanangel in forum Air Conditioning
    Replies: 1
    Last Post: 10-07-2009, 01:26 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •