    Need for Glycol



    We are replacing our ice water system with a chilled water system. The supplier says we have to use glycol since temp is 2C. Upto what temperature can we operate this R22 based system without using any glycol. Is 4-5C OK?
    Last edited by Hemant Anand; 23-07-2005 at 11:04 AM. Reason: spelling corrections



  2. #2
    Join Date
    May 2004
    Location
    england
    Age
    61
    Posts
    48
    Rep Power
    0

    Thumbs up Re: Need for Glycol

    welcome hemant, in the office building I look after we use large flooded systems using r22. the chilled water flow temp is set for 6 degrees centergrade. We have had it down to 5 degrees but any lower and we run the risk of bursting the tubes. remember the temperature in the evaporator will be lower than the leaving temperature of the water so I would be cautious about running a water chiller any lower than 4 or 5 degrees.

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Need for Glycol

    I would be cautious about running a water chiller any lower than 4 or 5 degrees.
    Hi Dill

    I think you meant without using glycol.

  4. #4
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Need for Glycol

    Conventional design says that 4.5 dC (preferred is 5 dC) is the lower limit for normal shell and tube design chilers. Special chillers are desingned which can get the LWT down to about 2 dC or a bit lower. One of this type is manufactured by Chester Jenson or Mueller Co. in the US. One name for this type chiller is a sliding film type.

    Ken

  5. #5
    Join Date
    Jul 2005
    Location
    Kuwait
    Age
    58
    Posts
    11
    Rep Power
    0

    Re: Need for Glycol

    Quote Originally Posted by TXiceman
    Conventional design says that 4.5 dC (preferred is 5 dC) is the lower limit for normal shell and tube design chilers. Special chillers are desingned which can get the LWT down to about 2 dC or a bit lower. One of this type is manufactured by Chester Jenson or Mueller Co. in the US. One name for this type chiller is a sliding film type.

    Ken
    Thanks a lot.

  6. #6
    Join Date
    Nov 2003
    Location
    holland europe
    Age
    66
    Posts
    78
    Rep Power
    21

    Re: Need for Glycol

    yes 4 degrees is possible with a good flow over in the tubes.
    if the r22 is inside the tubes you can go deeper as the ice will build around the tubes.
    why do you need to go lower?
    and if you need 0 why not use ice slurry
    at sea we make the slurry and it is nice 0 with some seawater around it.
    computer shooter