    Carrier 30HK 50 problem



    Dear Friends,

    I have problem with Carrier 30HK high discharge temperature problem as
    1. High discharge temperature 90'C
    2. High Side pressure 180psi
    3. Low side (After TXV) tmperature 4~6'C
    4. Low side pressure 60~80psi

    Before above found out, there was a low pressure at cut off switch. So, I top up the refrigerant from low pressure switch port which is located near piston which is gone down to negative pressure during operation. After top up it reached to 5psi.

    There was different pressure between pressure differential switch point measurement (Negative pressure) and suction pressure gauge display (5psi).



  2. #2
    Join Date
    Jun 2008
    Location
    TURKMENISTAN
    Age
    44
    Posts
    14
    Rep Power
    0

    Re: Carrier 30HK 50 problem

    ur refrigerent is r22? so how it can be 90 'C at this pressure? two possibilies: 1. ur temperature sensor defected. 2. there is problem in the compressor. u have to open pistons and u have to check valves, plate and the rest.

  3. #3
    Join Date
    Apr 2007
    Location
    The Netherlands
    Age
    67
    Posts
    20
    Rep Power
    0

    Re: Carrier 30HK 50 problem

    need more (running) parameters ie superheat and subcooling?, and of its stays running? i think maybe you've less refrigerant or a restriction in the system, but needs more information

  4. #4
    Join Date
    Nov 2010
    Location
    Singapore
    Posts
    7
    Rep Power
    0

    Re: Carrier 30HK 50 problem

    Thank,

    It used R-22 and I measure with calibrated thermometer from discharge pipe. I feel like it was choked in strainer or solenoid valve. Temperature was too much different between condenser inlet and outlet.

    Do you have any idea to check the system?

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Carrier Chillers
    By Ed Burris in forum Technical Discussions
    Replies: 6
    Last Post: 27-03-2010, 02:00 AM
  3. carrier ultima 53 problem
    By tito in forum Trouble Shooting
    Replies: 0
    Last Post: 08-08-2009, 04:07 PM
  4. Saunier Duval Problem
    By mallorcanangel in forum Air Conditioning
    Replies: 1
    Last Post: 10-07-2009, 01:26 AM
  5. Furance problem
    By ALONEI in forum Trouble Shooting
    Replies: 10
    Last Post: 14-05-2008, 11:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •