25-11-2010, 10:32 PM #15
Re: 7 Subcool & Superheat Problem Scenarios
Well, lets see. For #3, 2k sub and 10k super...capillary system working hard, high condenser and evap loads.... OR, tev system with high evap load. Either way,not enough info for correct assessment. To be bold, 2k sub could represent undercharged and shot condenser with 2 of 3 fans dead on a cool day. Mike.