    Searle Celler Cooler



    Hi not much experience on this equipment ,it is in mates pub and seems to have been running quite a while with little or no gas.was on r12 which ive tried to replace with 413 but system will only run for about a minute or less before shutting off then comes back on after 10 or more minutes then does same again.So its proving difficult to regass or access ,compressor seems ok but when it cuts in theres not alot of movement on gauges whats best way to check compressor is ok.Any help welcome.Cheers.



  2. #2
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: Searle Celler Cooler

    Have you identified and corrected the gas leak, have you liquid charged the receiver, are you sure that the TEV is not closed down or even the heat exchanger blocked (had that quite a few times) When it stays off for 10 minutes what exactly is it off on, LP, HP, T/stat, klixon, contactor overload?

  3. #3
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Searle Celler Cooler

    Did you change the filter/drier?
    Did you vacuum the system properly?
    It sounds like it is going off on H/P switch,
    Is the cond clean and undamaged?
    Did you liquid charge the gas?

    If the comp has stop valves on it you can shut the suction valve and make sure the comp pulls a vac. Then let it sit for a moment to make sure it doesn`t rise again. This would prove the comp is probably ok... hope this helps.
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  4. #4
    Join Date
    Apr 2005
    Location
    INDIA
    Age
    63
    Posts
    84
    Rep Power
    20

    Re: Searle Celler Cooler

    Quote Originally Posted by donetello
    Hi not much experience on this equipment ,it is in mates pub and seems to have been running quite a while with little or no gas.was on r12 which ive tried to to check compressor is ok.Any help welcome.Cheers.
    Mr, dutlo,
    a, Have U changed the oil to polyol easter (poe) for R12 mineral oil is used,
    b, Check up the AMPS drawn by the compressor,

    I advice U to take help of a techinican, HELP him while he his working, U can learn much more easier,I strongly feel U R COMPRESSOR IS SHORT CIRCUITED OR FAILURE OF RELAY / OLP!
    regards,
    beni joseph,

  5. #5
    donetello's Avatar
    donetello Guest

    Re: Searle Celler Cooler

    All i can tell you all is the liquid line gets very hot when operating whilst the suction remains warm, the gas appears to be circulating through the system but not sure 100%.Ive not changed drier or TEV ,trying first to make certain compressor is ok before fitting new parts,dont think there is any shut off valves on comp to check its pulling and holding a vac is there another way to check comp is ok.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Searle Celler Cooler

    system will only run for about a minute or less before shutting off
    Sheech - such a small amount af time to make a diagnosis !

  7. #7
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Searle Celler Cooler

    If the liquid line gets v hot then a safe assumption would be that the comp is ok .
    make sure the cond is clean and is getting a good air flow
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Searle Celler Cooler

    Quote Originally Posted by donetello
    ...system will only run for about a minute or less before shutting off then comes back on after 10 or more minutes then does same again.So its proving difficult to regass or access ,..........................
    If the system was evacuated properly then the recharging should not have been a problem.

    compressor seems ok but when it cuts in there's not alot of movement on gauges ..
    The perhaps there is a shortage of refrigerant.
    the liquid line gets very hot when operating whilst the suction remains warm,
    What is the state of the refrigerant charge ?

    Please give us some readings so that we have something to work with.

    If the compressor is shutting down after about 10 minutes and the pipes are hot then we get back to a refrigerant charge problem. Are there any pressure switches in the circuit which are operating when you run it ? But, to be honest it sounds like the compressor Klixon is operating due to overheating; which comes back to the refrigerant charge.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Searle Celler Cooler

    he says it runs for a minute..........

    Therein lies the clue.......

    Compressor stops.

    What makes it stop???

    yes...............a control................

    Donatelo............tell us which one????
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  10. #10
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Searle Celler Cooler

    Quote Originally Posted by donetello
    All i can tell you all is the liquid line gets very hot when operating whilst the suction remains warm, the gas appears to be circulating through the system but not sure 100%.Ive not changed drier or TEV ,trying first to make certain compressor is ok before fitting new parts,dont think there is any shut off valves on comp to check its pulling and holding a vac is there another way to check comp is ok.
    R 413 runs higher head pressure than r 12.Maybe unit is tripping on hp control. Certainly sounds like it.

    Warm dryer lack of condenser airflow? Although all the old commercial r12 systems that I have seen with drop ins seem to run a warmer dryer than previously.

  11. #11
    Join Date
    Aug 2004
    Location
    Holland
    Posts
    55
    Rep Power
    20

    Re: Searle Celler Cooler

    Here is a link to the specs of R413a

    http://www.isceon-refrigerants.co.uk...brochure49.pdf

    If the liquid line is hot, generaly there is a condensation problem.
    If there is a condensation problem, then normaly the evaporator wil not function fully and suction will not become cold.

    So take 2 bucket of water and clean the condensor, then restart, take readings and fix it.

    Victor

Similar Threads

  1. air cooler uneven distribution check
    By Lc_shi in forum Fundamentals
    Replies: 5
    Last Post: 17-06-2006, 12:47 AM
  2. Small Searle Cooler
    By Abe in forum Commercial
    Replies: 9
    Last Post: 27-01-2006, 06:07 AM
  3. Thermo-syphon Oil Cooler
    By B.B. in forum Industrial
    Replies: 5
    Last Post: 31-10-2005, 01:25 PM
  4. Searle cellar cooler control problem
    By iceman007 in forum Electrical
    Replies: 6
    Last Post: 06-07-2004, 08:57 PM
  5. Searle Evaporator
    By Abe in forum Commercial
    Replies: 1
    Last Post: 07-12-2002, 11:59 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •