    I need your help



    in the work place theres a produce case hussman multiple decks (2) 8 fts lengh 2 fans 1 for evaporator coil,the equipment is charged with the right charged but i cant get a low temp just 44 degrees (f) not less, so i dont know, if its that termostatic expansion valve is bad or some other problem, i hope your help thanks.



  2. #2
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: I need your help

    Quote Originally Posted by theicehunter View Post
    in the work place theres a produce case hussman multiple decks (2) 8 fts lengh 2 fans 1 for evaporator coil,the equipment is charged with the right charged but i cant get a low temp just 44 degrees (f) not less, so i dont know, if its that termostatic expansion valve is bad or some other problem, i hope your help thanks.
    Theicehunter, can you be sure the evaporator coil is completely free of ice? Gas type/pressure etc required.. mike.

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: I need your help

    The setpoint is?

  4. #4
    Join Date
    Oct 2009
    Location
    USA
    Age
    67
    Posts
    28
    Rep Power
    0

    Re: I need your help

    I presume the sight glass is full. After checking the evap coils for no ice,
    Check the super heat at each coil,
    Check thermostat setting,
    Check LP cut-out setting.