trane RTAC Chiller
Hi,
anybody can please explain me about rtac screw chiller minimum and maximum limit of below
OIL TEMP MAX AND MIN
INTERMEDIAE OIL PRESSURE MIN AND MAX
REFRIGERANT LEVEL MIN AND MAX
APPROCH TEMP MIN AND MAX
-
26-10-2010, 08:20 PM #2
Re: trane RTAC Chiller
hi all , do modern w-chillers have a temp sensor to detect if a cc heater has been on, or if the oil is hot enough?
-
26-10-2010, 10:14 PM #3
Re: trane RTAC Chiller
hi again,yes these units do monitor oil temp and will prevent starting until correct temp is reached.
THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
27-10-2010, 07:37 AM #4
Re: trane RTAC Chiller
Hi, Max oil temp is 93°C. If the female is not loaded and the oil temperature is near cut out then CH530 energize female in order to decrease oil temp till 77°C. As a rule of thumb normal oil pressure, when female is loaded, should be approximately 1Bar below high pressure. Specifically the oil pressure is controlled by the following formula: {(High Pressure – Oil Pressure) / (High Pressure – Low Pressure)}. When the female is energized the result which generates a low oil flow alarm is 0,25. When the female is not energized the limit is 0,5. The refrigerant level can vary from -1” to +1” (-25,4mm to +25,4mm). Normal operation is at 0mm. The normal approach for this kind of evaporator (Falling Film) is about 1,5°C.
Hope I help.
Similar Threads
-
unloading Trane RTHA chiller
By aumeche96 in forum CommercialReplies: 1Last Post: 21-10-2010, 05:26 AM -
Trane chiller
By scrappy77 in forum CommercialReplies: 5Last Post: 22-08-2010, 08:51 PM -
Trane chiller problem
By dannycool in forum Air ConditioningReplies: 6Last Post: 08-04-2010, 11:31 PM -
Trane CVHE 450 R11 Centrifugal Chiller
By albertjoseph in forum Air ConditioningReplies: 4Last Post: 06-10-2008, 03:23 PM -
Connecting Trane Water chiller to air handling unit
By celtictech in forum FundamentalsReplies: 10Last Post: 08-03-2007, 06:14 PM