    F-Gas Regulations - installation



    I understand what pat of the Regs say with regard to a service engineer's tasks of pressure-testing and leak repairs, compressor changes or any component change which involves in opening up the system; we must make a return visit within 4 weeks to confirm there are no further leaks.

    But how does this affect the installation industry? Is a pressure test certificate and commissioning sheet enough, or are they also obliged to return within 4 weeks and ensure their newly installed system is leak free?

    Thanks


    If at first you DO succeed, try to hide your astonishment!!

  2. #2
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: F-Gas Regulations - installation

    The follow up actions / checks can be done the very same day by recording the relevant readings such as superheat subcooling air flow/temp etc

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: F-Gas Regulations - installation

    The repair must be ensured, but a newly installed system is implicitly leak tight by definition.

  4. #4
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: F-Gas Regulations - installation

    Quote Originally Posted by NoNickName View Post
    The repair must be ensured, but a newly installed system is implicitly leak tight by definition.

    That is my interpritation of the regs as well.

    A new install is, a new install and would not be left
    with a leak.

    The repair, maint, replacement or other work carried out is the one that requires a follow up.

    taz

    .

  5. #5
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: F-Gas Regulations - installation

    Thanks for the answers chaps. The question was posed to me today and I told him what I told you; but being in the service sector, it made me think.
    If at first you DO succeed, try to hide your astonishment!!

Similar Threads

  1. Installation of NRVS check valves
    By Josip in forum NH3
    Replies: 10
    Last Post: 02-12-2008, 01:33 PM
  2. F Gas regulations - New qulaifications regulations published.
    By Argus in forum Legal-Business-Marketing
    Replies: 17
    Last Post: 20-06-2008, 08:24 PM
  3. Replies: 4
    Last Post: 19-05-2008, 11:04 AM
  4. Q: Piping installation for Split Types
    By brianubaldo in forum Refrigerants
    Replies: 11
    Last Post: 30-04-2008, 02:23 PM
  5. New Regulations on F Gas
    By Argus in forum Legal-Business-Marketing
    Replies: 19
    Last Post: 17-01-2008, 07:55 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •