Thread: Daikin VRV III fault
07-10-2010, 12:34 AM #1
Good evening gents.
I have a site that has developed an 'E9' fault on a multi system.
Master unit: REMQ12P8Y1B
Slave unit: REMQ10P8Y1B.
My engineer has checked over the system and has located the fault to the subcooler expansion valve on the 'master' unit.
In the meantime he has set up emergency mode '38' to enable the slave unit to operate, but the system still keeps faulting. The command for this setting has been accepted but upon attempting to switch on the system via the ITC the system still registers the fault code 'E9' and the system will not operate.
Anybody came across this before?
Jase
07-10-2010, 10:31 AM #2
Re: Daikin VRV III fault
hey jase
ive had a similar problem with the vrv's and i also have the daikins service manual i looked up E9 and it can eitha be the electronic expantion valve playing up or the A1P PCB board so try running the board through the tests to make sure its not faulty,
pam
07-10-2010, 03:18 PM #3
if you put the unit in emergency operation then drop the power to master unit it shouldn't fault out
08-10-2010, 08:04 PM #4
Прошу помощъ, нужна новая версия Service Checker TYPE3 заранее благодарен.
Converted to English reads:
I ask помощъ, new version Service Checker TYPE3 thankful in advance is necessary.Last edited by frank; 09-10-2010 at 11:10 AM.
e4 fault code on daikin super inverter
By Improver in forum Air ConditioningReplies: 13Last Post: 24-03-2011, 04:58 PM -
Daikin r407c 2 pipe vrv ja fault code any offers?
By Contactor in forum Air ConditioningReplies: 11Last Post: 28-07-2009, 01:26 AM -
Daikin Split f3 Fault
By moondawn in forum Air ConditioningReplies: 18Last Post: 01-06-2009, 07:09 PM -
UA Daikin Fault Code
By jedi in forum Air ConditioningReplies: 2Last Post: 23-07-2007, 01:44 PM -
u4 fault on a Daikin inverter
By phil17 in forum Air ConditioningReplies: 39Last Post: 05-02-2007, 02:41 AM