    Issue with a Searle evaporator



    Hi chaps, new to this but:

    Have been commissioning a 4 deg C pharmaceutical coldroom a Searle KEC40 cooler & matched Danfoss condensing unit. There is an identical room on the floor above which works fine but can't get the current one to meet the duty.

    Evap temp is way too low - about minus 12°C when should be maybe minus 2°C. The lower two thirds of the cooler tubes ice up whereas the top ones don't seem to be receiving any refrigerant (R404A).

    Expansion valves appear to be sized ok. The distributor splits 3 ways. Are there any known issues with distributors or anything similar?

    I'm assured the system was nitrogen purged while brazing etc but didn't witness it personally.

    Any input would be useful!



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Issue with a Searle evaporator

    Is distributor positioned vertically?

  3. #3
    Join Date
    Feb 2009
    Location
    bruges
    Age
    45
    Posts
    42
    Rep Power
    0

    Re: Issue with a Searle evaporator

    i would measure the superheat.Check the tev bulp , is it properly fixed on the suction line.Check if the tev is 404a.

  4. #4
    Join Date
    Sep 2010
    Location
    Derbyshire UK
    Age
    69
    Posts
    6
    Rep Power
    0

    Re: Issue with a Searle evaporator

    Yes, distributor is vertical with inlet at the top. Has to be a blockage in one of the three tubes? I think the next step is we change the coil - there are some other identical evaporators on site awaiting installation. Thanks for your input.

  5. #5
    Join Date
    May 2006
    Location
    aberdeen
    Posts
    124
    Rep Power
    18

    Re: Issue with a Searle evaporator

    what size of orifice has been used?.
    Is there a oil seperator/oil trap fitted?.
    What is the subcooling/superheat on codenser/evap/liquid line/ suction pipe?.
    happy hunting.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. EVAPORATOR leaked
    By James priyono in forum Air Conditioning
    Replies: 4
    Last Post: 23-05-2009, 10:19 AM
  3. Defrost cycle Searle Evaporator
    By Contactor in forum Trouble Shooting
    Replies: 4
    Last Post: 30-05-2007, 08:15 AM
  4. Searle Evaporator Heaters
    By Abe in forum Commercial
    Replies: 14
    Last Post: 31-12-2005, 10:24 AM
  5. Searle Evaporator
    By Abe in forum Commercial
    Replies: 1
    Last Post: 07-12-2002, 11:59 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •