    The limit to any compressor discharge temperature is 225 degrees F. If the discharge temperature gets higher than 225 degrees, the system may start to fail from worn rings, acid formations, and oil breakdown. Remember, if the discharge temperature is 225 degrees, the actual discharge valve will be about 75 degrees hotter. This will bring the actual compressor’s discharge valve to 300 degrees. It is a known fact that most oil may start to break down and vaporize at 350 degrees. If this occurs, serious overheating problems will happen. And, since compressor overheating problems are today’s most serious compressor field problems, service technicians must always monitor compressor discharge temperatures and keep them under 225 degrees. You can record superheat at any time but the biggest effect is when your fully loaded, you can always put a recorder with the senseo mounted about 6" from the discharge service valve. Some of the reasons for high compressor discharge temperatures are:
    High condensing pressures;
    Low suction pressures;
    High compression ratios; and
    High compressor superheats.
    11,024
    Re: Superheat
    Quote Originally Posted by frank
    Comments Please
    NO !
    Oh, OK, it seems to be a valid comment and something that we should all be aware off.
    One is tempted to ask whether additional safeties should be fitted to compressors to monitor discharge temperatures to protect the compressor. Yes, I am aware that they are fitted but is that ALL compressors ?
    Jun 2005
    California
    394
    Re: Superheat
    Botrous: When your in superheat there is no PT relationship so head pressure cutout is not the answer you need to put a tenperature control with a senser about 6" from service valve to cutout the compressor and set it for about 250*F
  1. TXV Superheat
    By Gary in forum Trouble Shooting
    Last Post: 24-04-2011, 02:51 PM
  2. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Last Post: 25-04-2010, 07:43 PM
  3. TEV superheat setting and low temperatures
    By DaBit in forum Fundamentals
    Last Post: 01-03-2010, 02:11 AM
  4. Superheat debate
    By zolar1 in forum Technical Discussions
    Last Post: 08-02-2008, 09:57 PM
  5. Superheat
    Last Post: 23-08-2004, 05:54 PM