Should oil and discharge pressure be close to same?
Compressor #1 sab 163 rotary screw..... discharge 140 psi
oil pressure 125 psi
Compressor #2 discharge and oil pressure are the same which i think is correct .
12-09-2010, 02:43 PM #2
Re: oil pressure
Hi Stan?
I have never really paid much attention to the differential between the discharge pressure and the oil pressure.
The really relevant one is the oil pressure diff.
As measured across the oil filter, usually with a Oil diff max of 1 bar.
Have you checked your transducers lately?
Cheers Grizzly
12-09-2010, 05:35 PM #3
12-09-2010, 06:23 PM #4
Re: oil pressure
On screw compressors, oil pressure should be the same as discharge pressure. If there is a difference of about 15 psi, oil filters should be changed.
I am not always right, but I'm never wrong!
12-09-2010, 06:49 PM #5
12-09-2010, 07:00 PM #6
Re: oil pressure
12-09-2010, 09:18 PM #7
Re: oil pressure
I cannot advise further at the moment as I don't have any plant logs at home.
But if you don't get further advise from on of the other guys.
I will check the details when next on-site.
Has this problem just occurred?
Or has there always been a difference?
Only there is a factory set oil pressure regulator within the Oil circuit.
Just maybe there has always been a difference between the 2?
Cheers Grizzly
15-09-2010, 12:19 AM #8
Re: oil pressure
Hi.
Your compressor dosent have an oilpump, or better the oil pump i sonly for the start sequence - pre-lubrication, your compressor only starts up if it has oil pressure, as the comrpessor starts the pressure on the oil goes near the dicharge. an oil separator is mounted on the dicharge side, so de pressure your mesuring is normal.
whats forces the oil to move in the system after start is the high pressure. Am I correct?
That compressor comes with a 3 way valve in oil pipping for temperature control. Also check that.
15-09-2010, 08:56 AM #9
Re: oil pressure
24-09-2010, 03:41 PM #10
Re: oil pressure
Have a york dxs45 compressor running very hot along bottom of compressor, even into the suction end. Fla% is 47 at 91A. It is at 75 steps, have 10vdc to cap valve should be fully loaded. Oil level is only into the bottom SG after an hour of runtime. Have six of the same compressor, this is the only one doing this. Any insight on this.
25-09-2010, 01:23 AM #11
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
NVQ 3 online test
By Burrah Boy in forum TrainingReplies: 7Last Post: 28-10-2009, 08:35 PM -
Effect of inverter on Pressure Ratio
By GIB in forum Air ConditioningReplies: 6Last Post: 03-10-2009, 01:54 PM -
How can I reduce evaporator pressure?
By mansari in forum FundamentalsReplies: 29Last Post: 05-09-2009, 01:59 AM -
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM