    Crankcase Pressure Regulator Valve



    HI. I`m fairly new to this.but does any one know what the Crankcase PRV is supposed to set at ? and if not set correctly would it cause compressor to ice up on the end when system is going thru defrost cycle. This is for a 5 horse power copeland hermatic compressor used for a reach in grocery store freezer display. 404A *****



  2. #2
    midnight50's Avatar
    midnight50 Guest

    Re: Crankcase Pressure Regulator Valve

    the way u need to set it up is to use your gauges and put about 100psig into the suction line and adjust valve until u get compressor to RLA amps

  3. #3
    Join Date
    Jun 2010
    Location
    USA
    Posts
    89
    Rep Power
    14

    Re: Crankcase Pressure Regulator Valve

    why is my suction line freezing up and compressor sweating when it goes into hot gas defrost? I thought it was because the PRV was not set right

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Crankcase Pressure Regulator Valve

    Have a read up on CPR vavles here http://www.parker.com/portal/site/PA...RCRD&stpoint=B

  5. #5
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Crankcase Pressure Regulator Valve

    Quote Originally Posted by jakb21599 View Post
    HI. I`m fairly new to this.but does any one know what the Crankcase PRV is supposed to set at ? and if not set correctly would it cause compressor to ice up on the end when system is going thru defrost cycle. This is for a 5 horse power copeland hermatic compressor used for a reach in grocery store freezer display. 404A *****

    You need to understand what is does first.

    There are a few pressure control valves that can be
    fitted to the suction but they do different
    things for different aplications.

    There are crankcase pressure regulators (CPR) and then
    there are evaporator pressure regluators (EPR), to name two.

    Do not confuse the two..

    The CPR protects the compressor from too much suction pressure
    Some systems with multiple evaporators and comps use them to
    stop the suction pressure getting too high. It is basicaly to protect
    the comp in extreme situations like defrost and startup.

    The EPR regulates the pressure inside the evap purly
    for temp control in the evap itself.

    Nether are designed to prevent liquid but both will affect pressures
    and therfore temps inside the suction and back to the comp.

    You need to find why your suction is freezing. Do not think that a
    freezing suction automatically means liquid. It can mean the suction
    is below freezing and that will happen with low temp and some medium
    temp systems. Remember that the evap temp of a 404 freezer will be
    about -35 degC ( - 30 degF in your money ) so the suction will freeze
    up with just suction vapour returning.

    All the best

    taz

    .
    Last edited by taz24; 25-08-2010 at 11:46 AM.

  6. #6
    Join Date
    Jun 2010
    Location
    USA
    Posts
    89
    Rep Power
    14

    Re: Crankcase Pressure Regulator Valve

    thanks for your help guys

  7. #7
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Crankcase Pressure Regulator Valve

    you have liquid coming back
    mmm to beer or not to beer...........lets drink breakfast

  8. #8
    Join Date
    Jun 2007
    Location
    South Africa
    Age
    66
    Posts
    120
    Rep Power
    17

    Re: Crankcase Pressure Regulator Valve

    Suction line freezing and compressor sweating does not indicate liquid flood back.

    What is the suction superheat?

    Semi Hermetic Compressors can show white frost all over the compressor motor area, up to close to the heads, without liquid coming back.

    Determine suction superheat, which should be 5 deg C minimum.
    I am not always right, but I'm never wrong!

  9. #9
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Crankcase Pressure Regulator Valve

    if hes got frosting after the cpr during defrost superheat of tx has nothing to do with it.
    5 deg c superheat in low temp system lol
    mmm to beer or not to beer...........lets drink breakfast

  10. #10
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: Crankcase Pressure Regulator Valve

    jakb21599,
    Frosting on the suction after the Crankcase Pressure Reg on hot gas defrost is normal,i have seen it a on all the hot gas defrost systems i installed,,,it's normal,,,,set the C/P/Reg at compressor full load amps,,,ignore the pressures.
    Lawrie

Similar Threads

  1. How to Design Refrigeration Systems
    By US Iceman in forum Fundamentals
    Replies: 63
    Last Post: 24-07-2008, 04:27 PM
  2. High Deferential Oil Pressure Alarm
    By NNNNNN in forum Trouble Shooting
    Replies: 27
    Last Post: 24-12-2007, 01:06 PM
  3. Liquid Overfeed Systems
    By US Iceman in forum NH3
    Replies: 151
    Last Post: 08-03-2007, 05:34 AM
  4. Crankcase Pressure Regulator
    By Abe in forum Technical Discussions
    Replies: 32
    Last Post: 10-09-2006, 01:56 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •