    charging split systems



    where do i find the formulas for figuring how much refrigerant to add for certain tubing lengths. like if you have a 40 foot lineset 3/4 and 3/8 i need to know how to add exact amount of refrigerant. you measure from the condensing unit to the metering device to determine total length right?



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: charging split systems

    You need the manufacturers info on this one as modern splits are critically charged normally xxxgrams per meter for every meter over a certain length

  3. #3
    Join Date
    Aug 2010
    Location
    usa
    Posts
    14
    Rep Power
    0

    Re: charging split systems

    thanks for the info

  4. #4
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: charging split systems

    the liquid line on modern splits is not a liquid line it is an expansion line so you need the maufactures info for the corect charge

Similar Threads

  1. Vrv
    By tgoonter in forum Air Conditioning
    Replies: 4
    Last Post: 11-01-2011, 06:25 AM
  2. Pressure testing for leaks on split a/c systems
    By mrchatts in forum Air Conditioning
    Replies: 46
    Last Post: 08-04-2010, 10:02 AM
  3. Sensible Heat Factor / capacity of Inverter split Systems at part load?
    By Greengrocer in forum Technical Speculations
    Replies: 31
    Last Post: 09-02-2009, 04:57 PM
  4. york split systems
    By SUBCOOLING in forum Air Conditioning
    Replies: 19
    Last Post: 23-05-2008, 08:36 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •