20-08-2010, 07:48 PM #1
charging split systems
where do i find the formulas for figuring how much refrigerant to add for certain tubing lengths. like if you have a 40 foot lineset 3/4 and 3/8 i need to know how to add exact amount of refrigerant. you measure from the condensing unit to the metering device to determine total length right?
-
20-08-2010, 07:51 PM #2
Re: charging split systems
You need the manufacturers info on this one as modern splits are critically charged normally xxxgrams per meter for every meter over a certain length
-
20-08-2010, 07:54 PM #3
Re: charging split systems
thanks for the info
-
20-08-2010, 10:28 PM #4
Re: charging split systems
the liquid line on modern splits is not a liquid line it is an expansion line so you need the maufactures info for the corect charge