    MCB rating



    hi guys,

    anyone know whats the reading mean on the MCB(Eg: B6.B16,B20,B32) mean? And some of the alphabet start with A6 and other start with c....which one should i choose for a A/c unit ...9000btu...?? thank very mch for those who reply for my curiousity



  2. #2
    rbartlett's Avatar
    rbartlett Guest

    Re: MCB rating

    6/16/20/32 relates to the current rating of the c/b

    a.b.c.d relates to the inrush trip caracteristics of the fuse

    http://www.tlc-direct.co.uk/Technica...bution/Mcb.htm

    a 230v 9k split -unless inverter- I would use D16 or C16

    cheers

    richard

  3. #3
    Join Date
    May 2005
    Location
    SPORE
    Age
    53
    Posts
    20
    Rep Power
    0

    Re: MCB rating

    tks richard! this really help for new technician like me..

  4. #4
    rbartlett's Avatar
    rbartlett Guest

    Re: MCB rating

    did you follow the link?

    "In some cases such even these MCBs may not be sufficient when Compressor motors are used and a type D MCB may be necessary. However, caution should be practised because the characteristics for these MCBs may make compliance with the Wiring Regulation difficult without a change in the specifications of the other equipment. "

    chers

    richard

  5. #5
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: MCB rating

    Richard,


    I have found a type " C " suitable .
    On an install last week, the sparky failed to turn up, I couldnt hang around so connected the system to the main consumer unit.

    It was crabtree............there was one spare fuseway, so I went round all the wholesalers looking for a 32Amp Type C , Crabtree breaker.

    No luck,, it was an old obsolete type. all they could offer was a Wylex type with a similar fitting size.

    It was type B............I had to take the chance............I bought it and fitted it.

    Unit started up and is running ok.............

    I have ordered a type C............but am struggling to get one....

    Just hope this Type B, performs in the interim
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  6. #6
    Join Date
    May 2005
    Location
    SPORE
    Age
    53
    Posts
    20
    Rep Power
    0

    Re: MCB rating

    in singapore ...the supply voltage here is between 220v~240v...what about u guys here??i knew some of them uses 110v and i dont understand why they dont want it to be standardise throughtout the world...?

Similar Threads

  1. A question about energy efficiency rating in Europe
    By pcdata76 in forum Fundamentals
    Replies: 1
    Last Post: 22-05-2006, 10:17 AM
  2. Setting Overload
    By Abe in forum Electrical
    Replies: 11
    Last Post: 06-01-2006, 01:53 PM
  3. Horse power rating
    By Argus in forum Air Conditioning
    Replies: 0
    Last Post: 03-02-2005, 10:52 AM
  4. Compressor back pressure rating
    By Cary in forum Fundamentals
    Replies: 9
    Last Post: 05-12-2004, 08:42 AM
  5. What rating standards are used?
    By baker in forum Technical Speculations
    Replies: 2
    Last Post: 03-02-2004, 03:27 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •