    Unhappy New scroll shuts off after one minute!! Restart after 2??



    Just installed a new 5 ton single phase Carlyle scroll compressor. started up and rans OK for 30 seconds. then shuts down for two minuts??? restarts then shuts down. changed all the stat componets. started with and with out potental relay.
    230V single phase 19.5 amps, low sided 60 psi high 200 psi.
    Old compressor was working fine. just had a stress crack in the compressor body (4 years old).



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: New scroll shuts off after one minute!! Restart after 2??

    And your question is???

  3. #3
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: New scroll shuts off after one minute!! Restart after 2??

    Maybe the problem is thermal overload tripping by the internal protection?

    Maybe is working in a hard regimen which the motor is not prepared for.

    What's the nominal and operational current? 19,5 Amps is nominal or absorbed? What's the other?
    To make progress is never good enough, I want to do better and better and better

  4. #4
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: New scroll shuts off after one minute!! Restart after 2??

    Request from the vendor the correct starting equipment (and wiring schematics) for his compressor.

  5. #5
    Join Date
    Mar 2005
    Location
    New Zealand
    Age
    43
    Posts
    64
    Rep Power
    20

    Re: New scroll shuts off after one minute!! Restart after 2??

    You need to carry out basic diagnostics and see what is stopping the compressor, has to be something on the control circuit telling it to stop, i'm sure the answer is right in front of you.

  6. #6
    Join Date
    Feb 2009
    Location
    UK
    Posts
    14
    Rep Power
    0

    Re: New scroll shuts off after one minute!! Restart after 2??

    Discharge klixon?

  7. #7
    Join Date
    Feb 2009
    Location
    bruges
    Age
    45
    Posts
    42
    Rep Power
    0

    Re: New scroll shuts off after one minute!! Restart after 2??

    check compr LRA amps check compr amps

  8. #8
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: New scroll shuts off after one minute!! Restart after 2??

    ...or it's passing a small current by some of windings directly to earth. Does the differential switch is tripping?
    To make progress is never good enough, I want to do better and better and better

  9. #9
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: New scroll shuts off after one minute!! Restart after 2??

    Hi Cygani.
    Welcome to the forum.
    Does this compressor have a control unit.
    Or what make condensing unit is it fitted to?
    It's just I cannot fathom what size system this comp would be attached to.

    Therefore whether start delay and anti recycle timers are relevant?
    More info is needed.

    If it is indeed purely stand alone then the guys above have the logical answer covered.
    Cheers Grizzly

Similar Threads

  1. Digital Scroll VRF Systems & Inverter Systems
    By weeliang82 in forum Air Conditioning
    Replies: 22
    Last Post: 16-11-2010, 04:07 PM
  2. Scroll compressor for Freezing application
    By georgedvf in forum Technical Speculations
    Replies: 18
    Last Post: 08-04-2010, 07:24 PM
  3. Digital scroll
    By archibaldtuttle in forum Commercial
    Replies: 3
    Last Post: 06-01-2010, 05:27 PM
  4. copeland ZR scroll vs VR scroll
    By Lc_shi in forum Technical Speculations
    Replies: 7
    Last Post: 03-09-2008, 04:27 PM
  5. Dual Scroll Compressor
    By ernestlin in forum Technical Discussions
    Replies: 7
    Last Post: 27-06-2006, 04:14 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •