    Y room 2 n 3 have 70psi when both unit swith on??



    eariler i went to a client house to troubleshhot a 3 in 1 sanyo unit...

    *room 1 - individual compressor (no problem)

    *room 2 n 3 - share compressor

    *room 2 A/C switch on only
    - gas pressure:70psi (offcoil 10-12degre celcius)

    *room 3 A/C switch on only
    - gas pressure:70psi (offcoil 10-12degre celcius)

    *room 2 n 3 A/C switch on
    - gas pressure:70psi (offcoil 19-20degre celcius for both room)
    - piping size and length : no problem



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Y room 2 n 3 have 70psi when both unit swith on??

    Are there any solenoid or electronic valves controlling the gas flow to room 2 n 3 ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Y room 2 n 3 have 70psi when both unit swith on??

    That sounds like a mis matched system which is how some of these multi spits work.

    If you look at the duty available from some Daikin indoor units when connected to a multi split they show a reduced duty when all evaps are on. I'll bet the twin split compressor is rated at 2/3rds of the capacity of both indoor units added together.

    How about posting some name plate ratings Ong

  4. #4
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    57
    Posts
    164
    Rep Power
    19

    Re: Y room 2 n 3 have 70psi when both unit swith on??

    [Hi
    Whats the model number of the system the indoors may be under sized to compensate for the outdoor capacity. Are the units under high load and whats the return air temp let me know i may be able to help

  5. #5
    Join Date
    May 2005
    Location
    SPORE
    Age
    53
    Posts
    20
    Rep Power
    0

    Re: Y room 2 n 3 have 70psi when both unit swith on??

    the owner have a new team of technician to check on the system.. so i do not have the chance to check on the technical stuff...but anyway ... what actually is the faults that result to this outcome anyone came across this problem b4 n which to share with us his knowledge??

    a normal 2-1 system which i encounter:
    when 1 unit is switch on
    suction : 63 psi
    discharge : 115 psi
    offcoil : 13degree celcius for unit 1

    when both unit is on:
    suction : 85 psi
    discharge : 115 psi
    offcoil : 12degree celcius for unit 2

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Y room 2 n 3 have 70psi when both unit swith on??

    Quote Originally Posted by frank
    ...If you look at the duty available from some Daikin indoor units when connected to a multi split they show a reduced duty when all evaps are on...
    This is because evaporating temperature will increase - compressor can't hold any longer a sufficient low pressure - and so the cooling capacity of each evaportor will decrease (DT between gas and ambient decreases).
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Y room 2 n 3 have 70psi when both unit swith on??

    Quote Originally Posted by Peter_1
    This is because evaporating temperature will increase - compressor can't hold any longer a sufficient low pressure - and so the cooling capacity of each evaportor will decrease (DT between gas and ambient decreases).
    This is exactly what the figures Ong has posted shows
    a normal 2-1 system which i encounter:
    when 1 unit is switch on
    suction : 63 psi
    discharge : 115 psi
    offcoil : 13degree celcius for unit 1

    when both unit is on:
    suction : 85 psi
    discharge : 115 psi
    offcoil : 12degree celcius for unit 2
    Look at the increase in suction pressure

Similar Threads

  1. Daikin a/c units.
    By rick in forum Air Conditioning
    Replies: 59
    Last Post: 18-02-2008, 09:22 PM
  2. Problem with ducted Daikin
    By jutty in forum Trouble Shooting
    Replies: 8
    Last Post: 23-07-2007, 05:34 AM
  3. Check RooM Aircon Outdoor Unit gas pressure
    By ongahhuat in forum Air Conditioning
    Replies: 16
    Last Post: 29-08-2006, 12:12 PM
  4. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Replies: 10
    Last Post: 22-04-2005, 05:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •