    Smile Help needed for portable air conn please



    Hi all,

    my apologies if this question has already been answered but was unable to find it.

    I have a wa12000r portable air con unit. It was working fine until a couple of days ago when i tried to switch it off. It would not switch off and the compressor carried on running until I unplugged it. If i plugged it back in again straight away, the compressor would run straight away, without even pressing the on button.

    If it was left off for several hours and then plugged in and acted as normal, ie, nothing until i pressed the on button and then the fan came on and about 3 mins later the compressor. All fine.

    However, even when the set temperature was reached, the compressor did not switch, even when i altered the temperature to 32 C ( the room was about 18c). Again switching the off switch off only turned the fan off but not the compressor.

    I have made sure that the water has been emptied and that the radiator grills have been cleared off any dust etc.

    Any help or advice would be greatly appreciated. Many thanks in advance.



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Help needed for portable air conn please

    Sounds like a relay or thermostat contacts have become welded together. needs looking at by someone familiar with the operation of air con or someone who is good with control systems.

  3. #3
    nowwhat's Avatar
    nowwhat Guest

    Re: Help needed for portable air conn please

    Thank you for your response but if the contacts had become welded together, wouldn't the compressor run all the time? Thanks

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Help needed for portable air conn please

    Quote Originally Posted by nowwhat View Post
    It would not switch off and the compressor carried on running until I unplugged it. If i plugged it back in again straight away, the compressor would run straight away, without even pressing the on button.
    Sticky relay? whatever it is it seems to bypass the 3 minute anti cycle timer.

    Quote Originally Posted by nowwhat View Post

    If it was left off for several hours and then plugged in and acted as normal, ie, nothing until i pressed the on button and then the fan came on and about 3 mins later the compressor. All fine.

    However, even when the set temperature was reached, the compressor did not switch, even when i altered the temperature to 32 C ( the room was about 18c). Again switching the off switch off only turned the fan off but not the compressor.
    Sticky thermostat? whatever it is it seems to bypass temperature termination.

    Quote Originally Posted by nowwhat View Post
    Thank you for your response but if the contacts had become welded together, wouldn't the compressor run all the time? Thanks
    Maybe the control circuit is fubared, test relays and stats first to eliminate them, then most likely it needs new control circuit.

  5. #5
    nowwhat's Avatar
    nowwhat Guest

    Re: Help needed for portable air conn please

    Thank you, i shall try and check the thermostat and realy out.

  6. #6
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Help needed for portable air conn please

    PCB fault I think!

  7. #7
    nowwhat's Avatar
    nowwhat Guest

    Re: Help needed for portable air conn please

    Thanks for your inputs, I shall have a play with it this weekend.

  8. #8
    Mike-Wadham's Avatar
    Mike-Wadham Guest

    Re: Help needed for portable air conn please

    sounds like the pcb is damaged, can you isolate the components and test internally?

Similar Threads

  1. Autocascade refrigeration system: design verification needed
    By DaBit in forum Technical Speculations
    Replies: 3
    Last Post: 07-02-2010, 07:48 AM
  2. Bit of help needed.
    By Lenny_b in forum Training
    Replies: 1
    Last Post: 01-06-2009, 11:35 AM
  3. Help needed sourcing an evaporator
    By jimbo22 in forum Fundamentals
    Replies: 3
    Last Post: 30-10-2008, 09:11 AM
  4. Smart/As needed evap defrost?
    By dkemper in forum Fundamentals
    Replies: 6
    Last Post: 27-10-2008, 07:25 PM
  5. Replies: 17
    Last Post: 25-08-2003, 09:56 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •