    TXV fault



    Have the following problem
    air cooled water chiller with r22 refrigerant, compressor is two stages 50 & 100%, two condenser fans set to start due to cond press as follow:
    first fan on@12 bar, off@14bar
    second fan on@19bar,off@14bar
    when second fan start at cond press 19 bar and evap press 4 bar, immediately cond and evap press drop , evap press to 2 bar and cond press drop below 14 bar so after short time the fan stop, and both press for evap and cond goes up again, then fan is on again and so so
    second fan is keeping turning on and off, and pressure for both cond and evap change widely up and down
    superheat is high especially when comp is 100%, it reach 13 C
    subcool is 9 C, and sight class is full
    disch temp is 90 C
    when copm goes to 50% superheat is good
    I tried to open TXV very widly but no change on supht
    I removed the sensing bulb from the suction line and wait for result, and problem dissapeared

    Should I replace TXV???

    Thank you



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: TXV fault

    first fan on@12 bar, off@14bar
    second fan on@19bar,off@14bar
    A classic case of incorrect settings causing the system to hunt.

    Adjust the fan cycle pressure settings to smooth out the condensing pressures. Once the first fan comes on it should stay on and the second fan should cycle on/off with load.

    I don't think this is a fault with the TXV

  3. #3
    szbo_tomas's Avatar
    szbo_tomas Guest

    Re: TXV fault

    first fan immediatly on when chiller on and never off, so as you said second fan only will regulate the cond pressure
    which I did not mention that the chiller has two circuit each with two fans, and the mentioned setting which is factory setting is for both circuits, but the problem is only with one circuit
    with the other circuit when second fan on @ 19 bar cond press, that press drop down to about 16 bar and stay for long period at this

    Thank you

  4. #4
    Join Date
    Jun 2005
    Location
    australia
    Age
    54
    Posts
    6
    Rep Power
    0

    Re: TXV fault

    is water set temp within normal specs maybe stage 1 and 2 getting different loads

Similar Threads

  1. Daikin fault codes
    By Markie in forum Air Conditioning
    Replies: 16
    Last Post: 13-01-2009, 01:58 AM
  2. Chigo Cpa-09co Fault Codes? E4?
    By chigosimon in forum Trouble Shooting
    Replies: 5
    Last Post: 24-11-2007, 12:46 AM
  3. Diplomat 6528 Fault Code
    By Targus in forum Domestic
    Replies: 3
    Last Post: 31-10-2006, 07:43 PM
  4. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM
  5. Chiller Fault
    By iceman007 in forum Air Conditioning
    Replies: 2
    Last Post: 13-05-2006, 07:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •