    H.P switch testing



    Hi

    How do you all test H.P. switches and do you consider slowly winding in the H.P. valve as a safe method of testing.

    Many thanks

    Bernard



  2. #2
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: H.P switch testing

    Hi Bernard,
    I would use nitrogen to test them.
    I think that winding in the comp head stop valve would be a big no no . What would hapen if the h/p switch didn`t work and youre hanging over the comp with youre ratchet in hand trying to open it back up again and the hose burst?
    remember ..... be safe (get the app to do it lol)
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  3. #3
    Join Date
    Jul 2004
    Location
    england
    Age
    52
    Posts
    64
    Rep Power
    20

    Re: H.P switch testing

    Cane use ofn to test the switch, or a hand pressure pump form H.R.P. I always use ofn its alot better, plus can see on the hp gauge what it trips at.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: H.P switch testing

    Hi Bernard

    Most of the posts refer to testing the HP prior to fitting but you do need to soak test the HP every year during maintenance inspections. To do this we bypass the stat and let the compressor run until the HP trips. Adjustments are sometimes made to set the correct cut out dependant on the gas used.

  5. #5
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: H.P switch testing

    Hi Guys,

    I always check with OFN if fitting one, but for one that's already in use what you can do is set the switch lower than it's normally set at eg 300psi PSI on 404 and either cover the condenser or SLOWLY !!! front seat the discharge to see if it cuts out and check the calibration at a more sensible level. Then if it works at the set cut out you can re-adjust it.

    Regards

    Fatboy

  6. #6
    Join Date
    Jan 2004
    Location
    Quebec,Canada
    Posts
    10
    Rep Power
    0

    Re: H.P switch testing

    I consider slowly winding in the H.P. valve is a safe method.
    You can actually control/raise pressure couples pounds at a time.

  7. #7
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: H.P switch testing

    I would use nitrogen to test new HP switch.

    Also cover up condenser to bring in fans,and test HP switch, this is simulating proper running conditions.Also use this method to check thermal overload suspected of tripping prematurly.

    Quick check wind in discharge service valve. Make sure gauge is connected to keep eye on pressure.

  8. #8
    Join Date
    Apr 2005
    Location
    INDIA
    Age
    63
    Posts
    84
    Rep Power
    20

    Talking Re: H.P switch testing


    Mr, Bernard.

    connect the H.P switch to nitrogen cylinder which

    must have a max 300 psi regulator ( guage connected.)

    slowley open the regulator for requred pressure and set

    the switch , Is it easy ?


    beni joseph.

  9. #9
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: H.P switch testing

    Hi all

    I have always used ofn in the past but I recently had about 20 switches to test so I wound in the hp valve,I,ve been told there is a internal safety valve within the compressor which will pass straight into the suction if there is any problems.I suppose the advantages of not using ofn is less things to disconnect so less chances for leaks.Does anyone know at what pressure the internal valve works.

    Regards bernard

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: H.P switch testing

    http://www.refrigeration-engineer.co...=bypass+scroll from 09-09-2004, hey...my wedding date
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: H.P switch testing

    Hi peter

    I don,t understand what you mean please can you explain

    Regards bernard

  12. #12
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: H.P switch testing

    Quote Originally Posted by bernard
    Hi peter

    I don,t understand what you mean please can you explain

    Regards bernard
    What? My wedding date? LOL
    No, if you read through that thread, you will find the answers for your questions, at least for the scrolls compressors.
    Last edited by Peter_1; 23-05-2005 at 10:44 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  13. #13
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: H.P switch testing

    Hi peter

    Sorry my fault,this time I was refering to recips,I believe if the pressure gets to high that there is a valve inside the compressor that will blow and send the discharge straight into the suction?

    Regards Bernard

  14. #14
    Join Date
    Jan 2005
    Location
    Norfolk, U.K
    Age
    44
    Posts
    65
    Rep Power
    20

    Re: H.P switch testing

    the grasso comps i have on site have an overfow safety valve (releif valve) which opperates at 22.5 bar and as you say, it allows the discharge to bypass into the suction.

    We normally test our pressure switches every 6 months, testing the hp by closing the dicharge valve slowly.

    system using R22, hp cut out set to 17bar
    Last edited by ecclesk; 24-05-2005 at 10:36 AM. Reason: add more info

  15. #15
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: H.P switch testing

    Hi.

    Using OFN you have the risk of pushing non condensibles into the sytem.
    Testing adjustable switches can simply be done by dropping cut out below operating pressure,this will prove the switch is wired correctly and generates an alarm.As well as the switches contacts breaking.
    I would be reluctant in winding in discharge valves to test switches.

    Best regards. Mark

  16. #16
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: H.P switch testing

    Hi.

    Using OFN you have the risk of pushing non condensibles into the system.
    Testing adjustable switches can simply be done by dropping cut out below operating pressure,this will prove the switch is wired correctly and generates an alarm.As well as the switches contacts breaking.
    I would be reluctant in winding in discharge valves to test switches.

    Best regards. Mark

  17. #17
    Join Date
    Oct 2002
    Location
    australia
    Posts
    28
    Rep Power
    0

    Re: H.P switch testing

    to test h.p switches i usually just isolate/disconnect the condenser fans.
    p.s what's ofn?

  18. #18
    Join Date
    May 2004
    Location
    england
    Age
    61
    Posts
    48
    Rep Power
    0

    Re: H.P switch testing

    hi adam, ofn stands for oxygen free nitrogen or white spot as I used to call it. As you know it is an inert gas and being totaly moisture free it is ideal for testing hp switches, stopping oxidisation whilst brazing and good old pressure testing. dill. ps, as mentioned it is vital that all of it is removed from the system after use as it does not condense well and is brilliant at picking up water.
    Last edited by dill; 09-06-2005 at 12:53 PM.

  19. #19
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: H.P switch testing

    Adam

    Have a look here http://www1.boc.com/uk/sds/

  20. #20
    Join Date
    Oct 2002
    Location
    australia
    Posts
    28
    Rep Power
    0

    Re: H.P switch testing

    yeah, we just call it dry nitrogen. cultural differences

  21. #21
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: H.P switch testing

    The risk of non condensibles through using OFN on a pack via valves letting by,does not warrant the risk.

  22. #22
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: H.P switch testing

    I usually disconnect the condenser fans, pressure climbs slow and its easy to follow the increasing pressore.

    HP controlls should be tested at work conditions and not in a lab.

    chemi

Similar Threads

  1. Pressure testing for leaks on split a/c systems
    By mrchatts in forum Air Conditioning
    Replies: 46
    Last Post: 08-04-2010, 10:02 AM
  2. flow switch connection
    By afeef in forum The Trail of Tears
    Replies: 18
    Last Post: 23-12-2009, 06:55 PM
  3. RCV and HIGH PRESSURE SWITCH
    By abbasi in forum Fundamentals
    Replies: 3
    Last Post: 22-03-2006, 08:51 AM
  4. shower switch fault !
    By Krups in forum Electrical
    Replies: 10
    Last Post: 19-10-2005, 09:10 PM
  5. Oil Pressure Switch
    By Abe in forum Commercial
    Replies: 9
    Last Post: 15-03-2003, 11:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •