Air-Cooled_Low Discharge Superheat Alarm
McEnergy Air-Cooled
Both unit is for stand by use only. When the fresh start signal sent, "low discharge superheat" alarm occur only on circuit #1 after 30 minutes. After alarm reset, everything back to normal. apply to before it trip, manually switch off and then switch on back. Anyone got this kind of problem?
-
25-07-2010, 09:08 AM #2
Re: Air-Cooled_Low Discharge Superheat Alarm
to be sure you have to measure the super heat , discharge temp.
is the unit equiped with electronic exp device ?
if so check the lp temp sensor.
good luck