    Air-Cooled_Low Discharge Superheat Alarm



    McEnergy Air-Cooled
    Both unit is for stand by use only. When the fresh start signal sent, "low discharge superheat" alarm occur only on circuit #1 after 30 minutes. After alarm reset, everything back to normal. apply to before it trip, manually switch off and then switch on back. Anyone got this kind of problem?



  2. #2
    Join Date
    Feb 2009
    Location
    bruges
    Age
    45
    Posts
    42
    Rep Power
    0

    Re: Air-Cooled_Low Discharge Superheat Alarm

    to be sure you have to measure the super heat , discharge temp.

    is the unit equiped with electronic exp device ?
    if so check the lp temp sensor.

    good luck