Thread: Questions

  1. #1
    Dtime35's Avatar
    Dtime35 Guest

    Questions



    Hello I have been reading up on refrigerants and was wondering is there no way to make a system that uses them in a cold state always, so you can allow air to by pushed over the coils to be cooled? Do you have to have the compressor and valve? Basically can you take an enclosed area and make the refrigrant in it a cool form and keep it that way in the enclosed area?



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Questions

    No, you can't Dtime.
    And why? well,....nature laws or thermodynamics with a more scientifice term
    Two adds via Google
    http://www.freestudy.co.uk/thermodynamics/t2109.pdf
    http://www.freestudy.co.uk/thermodynamics/t5201.pdf

    have perhaps a look at http://www.freestudy.co.uk/thermodynamics2.htm for all their files
    Last edited by Peter_1; 22-05-2005 at 11:30 AM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Dec 2005
    Location
    Egypt
    Posts
    21
    Rep Power
    0

    Re: Questions

    hi dtime..
    what happens in any chiller is heat transfer the air is hot , the refrigerant is cold .
    air takes the cold temperature from the refrigerant and the refrigerant it self takes the heat from air ... so by time refrigerant will be just hot vapor

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Questions

    Sorry, perpetual motion has not been invented yet.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: Questions

    As long as the area/device being cooled can be warmer than the place the heat is discharged into, it can work without a compressor. I've seen that being used in laptops and certain high performance desktop/server computers. The idea is to boil a refrigerant (usually R134a or an alcohol) with the heat from the device being cooled, and then condense it with the heatsink. The refrigerant returns to the evaporator by gravity. Done right, it will work like a material with a very high thermal conductivity.
    Now, if you need the temperature to be lower, then you need a compressor.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Questions

    Sounds like the principle of a heatpipe.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Questions

    A thermosyphon loop could also be used for this, but again, the lowest achievable temperature is fixed by the heat sink temperature that the heat is transferred to. This seems to be the same thing star882 is talking about.

    You can do the same thing for heat recovery in air systems during the winter time. The lower dry bulb temperature provides a much lower heat sink temperature to recondense the refrigerant. However, most of these systems are dependent on gravity.

    So, the installation is critical to work properly.

  8. #8
    Join Date
    Dec 2005
    Location
    Johor
    Age
    62
    Posts
    151
    Rep Power
    19

    Re: Questions

    Impossible?????
    An impressive imaginative idea but lets be realistic.

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Questions

    abdulazman,

    What are your concerns with this? I have done this several times and it works very well.

    This is no different than the use of a thermosyphon for oil cooling on large screw compressors.

    Regards,
    US Iceman

  10. #10
    Join Date
    Dec 2005
    Location
    Spain
    Posts
    61
    Rep Power
    19

    Re: Questions

    Well designed pipework and a massive condenser.... whats the problem... Didnt somebody do this with, i think it was council offices in England. Had to force run the compressors once a week to keep the bearings lubricated.
    :cool: Calvo :cool:

  11. #11
    Join Date
    Dec 2005
    Location
    Spain
    Posts
    61
    Rep Power
    19

    Re: Questions

    It was a long time ago.... the only reason i remember is that we had the problems with the bearings in the compressors because the things were never run. A pricey install but if the end user has the foresight and the right duty requirements, a good system.
    :cool: Calvo :cool:

  12. #12
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Questions

    Enhanced heat transfer surface use depends on the film coefficients for each side of the surface. When using refrigerant to cool or heat air, the air film coefficient is much lower than the refrigerant side.

    Therefore there is little to be gained by using enhanced heat transfer surface on the refrigerant side.

    For water to refrigerant, the water film coefficient can be quite high, so enhancement on the water side would be beneficial. In this case, the refrigerant side enhancement can help.

    The lower film coefficient can be said to be the controlling limit, so if the enhancement is on the wrong side very little is gained at a potentially significant cost.

    The High-flux tubing is very interesting. One of the drawbacks to it is that you need some minimum temperature difference to start the nucleation and capillary effect of the sintered tubing. In some cases (from reports I have read) this type of heat transfer surface can take some time to reach it's full potential for heat transfer.

    If I remember correctly, the tubes must first heated to initiate the capillary action of the surface, then the entire surface must reach it's full potential for all nucleation sites on the tubing.

  13. #13
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Questions

    Thermosiphon cooling is old school and works very well. But you still have to have a heat sink to dump the heat in any case.
    Ken

  14. #14
    Join Date
    Dec 2005
    Location
    South East England
    Age
    56
    Posts
    155
    Rep Power
    19

    Re: Questions

    A thermo-syphon is used on the thermo-electric bottle cabinets I've been asked to carry out warranty work on recently. It's attatch to the hot side & looks very similar to a domestic fridge condenser. Don't know what the medium is inside the tubing tough.
    Noah had to leave the dinosaurs behind as they would've sunk the boat.

  15. #15
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Questions

    We looked at the High-Flux tubing from UOP for flooded ammonia chillers. It was an absolutely fascinating material, but too expensive for our use.

    It was actually cheaper to manufacture a larger prime surface exchanger, than the smaller one using the UOP enhanced tubes at the time.

    All of the nucleation/capillary stuff came from the research papers I reviewed when we were looking into this. It seems to me that in one case the researchers mentioned it could take up to one hour before the tubing performed at full potential.

    The increase was not due to the surface area of the tubing so much as it was the capillary action and the many nucleation sites on the tube due to the sintered finish. Similar to smooth tubing versus a tube with a rough finish.

    Another interesting item for enhanced heat transfer is made by Cal Gaven there in the UK. They are tube inserts called HiTran. It looks like a spring made from paper clips. Also very fascinating...

    We are off the original topic quite a bit, but worth mentioning.

Similar Threads

  1. Interview questions
    By zimbo in forum Chit Chat & Service Stories
    Replies: 16
    Last Post: 10-09-2008, 10:06 PM
  2. few questions
    By abbasi in forum Fundamentals
    Replies: 5
    Last Post: 16-07-2006, 11:28 AM
  3. some questions of air source hp
    By Lc_shi in forum Technical Discussions
    Replies: 3
    Last Post: 11-05-2006, 08:58 PM
  4. questions
    By parry in forum Chit Chat & Service Stories
    Replies: 17
    Last Post: 31-10-2005, 08:46 AM
  5. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •