    York YAEP chillers



    Can any one let me know if you are facing any problem with the leaving chilled water temperature from YORK chiller YAEP 6666. The chiller is not giving a constant outlet temperatur, it is ranging between 43 to 50 F.



  2. #2
    Join Date
    Jul 2010
    Location
    UAE
    Posts
    14
    Rep Power
    0

    Question Re: York YAEP chillers

    Hi Ary,

    Can you give the pick load operating readings of the chiller? It difficult to figure out without basis.


    Regards,

  3. #3
    ARY75's Avatar
    ARY75 Guest

    Re: York YAEP chillers

    Thanks Dennis for passing.
    Actually I`ve gone through York O&M manual, and it is clearly talking about the mixed water temperature from the two evaporators of one chiller, and there is a control range temperature. So I think the chiller is indeed designed like that. Can anyone confirm that, and what is effect on the whole system when the supply temperature is varying from 43F to 50F.

  4. #4
    Join Date
    Feb 2010
    Location
    uae
    Age
    48
    Posts
    39
    Rep Power
    0

    Re: York YAEP chillers

    Hi, initially ur mix water temp say 42, unit temp set pt be 43f - 45f with less diff will maintain the hedder temp, also check rate sensitivity, be kept min of 3.5- 3.7. If load constant like recidense bldg, rate sensitivity be kept 4 so loading of compressors will take more time duration.

  5. #5
    ARY75's Avatar
    ARY75 Guest

    Re: York YAEP chillers

    Thanks Muju
    now the fluctuation is less, but number of starts is high.
    The question here is that correct, i.e. to control the mixed water rather than leaving temperature.

  6. #6
    ARY75's Avatar
    ARY75 Guest

    Exclamation Re: York YAEP chillers

    I am almost sure now that there is a problem with this chiller. if anyone have the same chiller, he may check that.

Similar Threads

  1. York Chillers
    By N.Lewis in forum Air Conditioning
    Replies: 5
    Last Post: 17-11-2010, 07:36 PM
  2. YORK YAEP HIGH DESCH ERROR...PLS Help
    By webdrops in forum Trouble Shooting
    Replies: 7
    Last Post: 15-06-2010, 06:39 PM
  3. centrifugal chillers york
    By Magic in forum Technical Discussions
    Replies: 6
    Last Post: 12-11-2009, 06:08 PM
  4. york millenium recip chillers help
    By clarkster in forum Trouble Shooting
    Replies: 1
    Last Post: 25-07-2009, 10:50 AM
  5. york gs/ gsi chillers
    By GHAZ in forum Technical Discussions
    Replies: 1
    Last Post: 16-09-2007, 10:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •