Results 1 to 3 of 3
  1. #1
    ramachandrasg's Avatar
    ramachandrasg Guest

    Clean room ac load calculation



    Hi,

    How to arrive cooling load for clean room.

    For example: If clean room requires for certain air changes (100% FResh air) is say 10,000 CFM and room to be maintained at 73 Deg F. and outside air temperature is 96 deg F DB and 62 Deg F WB.
    Pls help how to arrive cooling load in TR for this??



  2. #2
    Join Date
    Jun 2009
    Location
    Scotland
    Age
    60
    Posts
    34
    Rep Power
    0

    Re: Clean room ac load calculation

    To determine the load you can use the following:

    [Enthalpy Outside Air- Enthalpy Inside Air] x Specific Gravity of Air x Vent Rate.

    As we use the SI system the conversions are as follows:

    10,000 CFM = 6990.108 meters cubed/hour
    96F = 35.6C
    62F = 16.67C
    74F = 22.78C [Since you have not stated RH = 50%]
    Spec Gravity of Air = 1.2
    Enthalpy Ouside Air [CIBSE Guide] 46.901
    Enthalpy Inside Air [CIBSE Guide] 44.869

    From formula above:

    [46.910-44.869] x 1.2 x 6990.108 = 17120.173 KJ/h

    Converting to Kw = 4.756.

    tmm

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Clean room ac load calculation

    Quote Originally Posted by ramachandrasg View Post
    Hi,

    How to arrive cooling load for clean room.

    For example: If clean room requires for certain air changes (100% FResh air) is say 10,000 CFM and room to be maintained at 73 Deg F. and outside air temperature is 96 deg F DB and 62 Deg F WB.
    Pls help how to arrive cooling load in TR for this??
    The total cooling load will need to be calculated to deal with building fabric gains, occupancy, lighting and equipment gains in addition to the ventilation load.

    Without further information from you it will not be possible to advise you correctly.

    I make the 100% fresh air load to be 106kW with a dt of 13K

    10000cfm = 4.719m3/s

Similar Threads

  1. load calculation
    By nonoy0041@yahoo in forum Supermarket Refrigeration
    Replies: 1
    Last Post: 14-11-2009, 08:30 PM
  2. clean room heat load
    By pramodpatil in forum Air Conditioning
    Replies: 1
    Last Post: 26-01-2009, 09:41 AM
  3. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •