Thread: what's missing...?
27-04-2005, 06:48 PM #1
what's missing...?
went to a daikin vam heat recovery 1500 today with the customer complaining of poor performance and dirt blowing out of the vents..
cheers
richard
27-04-2005, 08:19 PM #2
Re: what's missing...?
Don't they use some kind of heat exchange, a coil for instance?
Chemi
27-04-2005, 08:28 PM #3
Where in the hell is the heat recovery device ? where is the coil ???
27-04-2005, 10:13 PM #4
The heat exchanger element is missing also the pre filters,
I think on your 1500 model there are two chambers with heat exchanger elements
regards
bob
27-04-2005, 11:06 PM #5
poor performance? i'm not surprised, the fans will not be developing any pressure. you see, there is also supposed to be a cover plate, over where the heat exchanger should be.
i can't beleive nobody else spotted this.
cheers
eggs
28-04-2005, 06:42 AM #6
I took the covers off expecting to clean the filters and give them the once over...I was confused enough to ring daikin tech to double check :-/
The customer now has the task of tracing who did it -installers or last service company and prehaps more importantly why they were removed in the first place..this was only installed in late 2002
the Daikin guy reckons it's about 2k to replace the 4x heat exchangers and filters -seems a bit steep but who knows..?
still, we're in the clear and will just await the outcome.. ;-)
cheers
richardLast edited by rbartlett; 28-04-2005 at 06:45 AM.