    YORK YAEP HIGH DESCH ERROR...PLS Help



    Hi,

    i am facing problem that now a days in summer, at around 12-1 when the ambient temperature rise to around 40-43'C the chiller stops, and gives error of High desch.

    we checked the filter drier cores, gas , solenoid ,exv etc....everything seems to be normal & at around 3-4 pm when there is slight decrease in temperature the machines become good & keep o workinng.

    kindly advice what needs to be checked or done.

    the chiller is YAEP YORK.

    the chiller works for max 5 minutes & then stops.

    do i need to increase the programed data & if yes thenn i dont have code to edit that.

    kindly guide me as i may loose my job because of this problem.

    thanks



  2. #2
    Join Date
    Apr 2009
    Location
    Qatar
    Age
    44
    Posts
    13
    Rep Power
    0

    Re: YORK YAEP HIGH DESCH ERROR...PLS Help

    Well...the problem is soved through this forum as i found that the Discharge pressure cutout was set low by our rival contractor who handedover these chillers to us changed the discharge cutout settings.

    thanks any ways.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: YORK YAEP HIGH DESCH ERROR...PLS Help

    Check fan rotation.
    Clean condenser (wash).
    Measure condensation pressure, air in and out temperature and post what is HP alarm setting set on unit. You could do that when temperature is not that high, but few °C lower (before alarm is expected to occure).

  4. #4
    Join Date
    Apr 2009
    Location
    Qatar
    Age
    44
    Posts
    13
    Rep Power
    0

    Re: YORK YAEP HIGH DESCH ERROR...PLS Help

    thanks for the guidance. my problem is already solved....through the Code 7396...as i increased the high pressure cutout.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: YORK YAEP HIGH DESCH ERROR...PLS Help

    Quote Originally Posted by webdrops View Post
    thanks for the guidance. my problem is already solved....through the Code 7396...as i increased the high pressure cutout.
    Are you sure that you did not exceeded compressor operating limits and that someone has changed that value before?

    If commissioning engineer done that, you may also expect some other sabotage.
    Few times, contractors I worked for, asked of me to do the simmilar, but I refused.

  6. #6
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: YORK YAEP HIGH DESCH ERROR...PLS Help

    Quote Originally Posted by nike123 View Post
    Are you sure that you did not exceeded compressor operating limits and that someone has changed that value before?

    If commissioning engineer done that, you may also expect some other sabotage.
    Few times, contractors I worked for, asked of me to do the simmilar, but I refused.
    wow and i thought this only happens on our side of the globe!!!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: YORK YAEP HIGH DESCH ERROR...PLS Help

    Quote Originally Posted by goshen View Post
    wow and i thought this only happens on our side of the globe!!!
    Here is pretty bad!

  8. #8
    Join Date
    Sep 2009
    Location
    Cyprus
    Age
    64
    Posts
    110
    Rep Power
    15

    Re: YORK YAEP HIGH DESCH ERROR...PLS Help

    If u know who did that and sabotage the unit u should report that to local authorities and to Johnson Controls,because such actions damaging the name of the refrigerator engineers and the companies working for,and of course they engineer that carried out that sabotage is totally a moran

Similar Threads

  1. YORK YAEP recip chiller fault
    By chiller1 in forum Trouble Shooting
    Replies: 8
    Last Post: 04-06-2010, 10:41 AM
  2. Over charged system... what symptoms?
    By Clk320_Greg in forum Trouble Shooting
    Replies: 2
    Last Post: 19-10-2009, 06:25 PM
  3. York Chiller High Line Voltage Problem
    By shamyl in forum Electrical
    Replies: 5
    Last Post: 19-07-2009, 07:53 PM
  4. High discharge temp
    By paul_h in forum Air Conditioning
    Replies: 48
    Last Post: 06-05-2009, 11:10 AM
  5. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •