    Smile DX PAU & Air-cooled condensing unit



    would seek for help of how to design an appropriate A/C system for DX PAU & Aic-cooled condensing unit, air flow rate: 920L/s and on-coil 33C/65%rh max to 18C/65%rh min. supply air temp at 18C.


    vB Code is ON

  2. #2
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: DX PAU & Air-cooled condensing unit

    what's PAU?

  3. #3
    Join Date
    Jul 2004
    Location
    england
    Age
    52
    Posts
    64
    Rep Power
    20

    Re: DX PAU & Air-cooled condensing unit

    Might mean packaged airhandling unit ????????

  4. #4
    Join Date
    Jul 2001
    Location
    hong kong
    Age
    65
    Posts
    27
    Rep Power
    0

    Re: DX PAU & Air-cooled condensing unit

    it means primary air handling unit(fresh air handling unit), the cooling capacity is 15 R.T.
    vB Code is ON

  5. #5
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: DX PAU & Air-cooled condensing unit

    OK. Understand.
    you can apply DX coil or water coil to deal with the fresh air and you'd better use heat recovery tech to save energy.
    May you sepecify:
    OA (temp and humidity)
    SA (temp and humidity)
    RA (same as above)
    the ratio of fresh air etc.

    i'd like to offer my suggestions

    rgds
    lichuan

  6. #6
    Join Date
    Apr 2004
    Location
    Pakistan
    Age
    44
    Posts
    129
    Rep Power
    21

    Re: DX PAU & Air-cooled condensing unit

    CFM = 1980
    Capacity = 15TR
    Entering (DB/WB) = 91.4/81.3 (Fahrenheit) 65% RH
    Leaving (DB/WB) = 64.4/57.35 (Fahrenheit) 65% RH

    I am sorry nobody can design DX coil on these parameters as critical point cant be achieved however if leaving conditions are changed
    Say
    Amended Data
    CFM = 1980
    Capacity = 15TR
    Entering (DB/WB) = 91.4/81.3 (Fahrenheit)
    Leaving (DB/WB) = 58/57.35 (Fahrenheit)


    Then DX coil data will be

    5.57 Sq. ft, 8 rows (@350 FPM)

    I do a lot of designing for these DX coils and AHU’s and find it difficult to understand how u can get 65% RH at leaving conditions
    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: DX PAU & Air-cooled condensing unit

    I do a lot of designing for these DX coils and AHU’s and find it difficult to understand how u can get 65% RH at leaving conditions
    Hi Abbasi

    Perhaps he's looking for the DX coil for temperature control and then a humidifier to raise the RH back up

Similar Threads

  1. M I T S U S H I T A ac unit with no condensing unit
    By Chinua in forum Air Conditioning
    Replies: 2
    Last Post: 28-07-2006, 06:54 PM
  2. York/Bristol Condensing Unit
    By Abe in forum Commercial
    Replies: 1
    Last Post: 03-02-2003, 07:46 PM
  3. Matching Evaporator with Condensing Unit
    By Abe in forum Technical Discussions
    Replies: 12
    Last Post: 25-07-2001, 08:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •