Low condensing pressure on freezer, not pulling temp
I have a walkin freezer room thats not pulling temp. Got a call last night, freezer was at 3.2C. by the time I got there it was at -13.8. Checked out system. Everything seemed ok. sight glass full. discharge pipe roasting,suction pipe cold,liquid warm, condenser coil clean,evap coil clean. All fans running. Suction pressure 2bar,condensing pressure 11bar. Very little heat rejection from the condenser. Blocked the condenser coil pressure slowly rose to 17.5bar. unit pumped down slowly as well. Condensing unit is Maneurop. Compressor is a NTZ068A4LR1A. Would I be right to say compressor is on its way out? If compressor is gone would I be right in changing it to a Copeland scroll?? Thanks for any help
-
05-06-2010, 02:10 AM #2
Re: Low condensing pressure on freezer, not pulling temp
You don't mention the type of refrigerant?
It is important so we can make a jugement on the comp.
Have you done a pump test on the thing.
With gauges fitted front seat the suction service valve and see with the suction does.
It should go very low into a vac (lower than 15"hg about 20"hg to 30"hg), the lower the better and with the
comp off it should stay like that for a good few mins (you may need to do somthing to the lp
switch to allow it to pump into a vac).
coolrunnings
.Last edited by cool runings; 05-06-2010 at 02:12 AM.
-
05-06-2010, 03:01 AM #3
Re: Low condensing pressure on freezer, not pulling temp
TEV are designed for a certain pressure drop across the vav to feed liquid to the evaporator, reduce the delta p and you starve the evaporator.
-
05-06-2010, 05:40 AM #4
Re: Low condensing pressure on freezer, not pulling temp
the ultimate question!
what is your subcoolin, SC and superheat. SH?
its a must check.
-
06-06-2010, 12:07 AM #5
Re: Low condensing pressure on freezer, not pulling temp
Hope you've found the cause of your problem.
Slow pump down sounds like you might have an issue with valves in the comp. Like Cool Runnings said - do the pump-down test.
If you fit a scroll as a replacement, you may find you have to install other fun stuff like liquid injection for cooling - might make replacing the manuerop with an identical unit more attractive.
-
09-06-2010, 08:10 AM #6
Re: Low condensing pressure on freezer, not pulling temp
Check the refrigerant amount.
If the compressor head is roasting then you have very high compression ratio.
Probably there is not enough gas in the system.
CheersEven Einstein Asked Questions
-
09-06-2010, 05:13 PM #7
Re: Low condensing pressure on freezer, not pulling temp
Thanks for the replies. Did the pump down test and the unit barely made it into a vac. Turned off compressor and it never held. It came straight out. I changed the compressor for a copeland scroll with liquid injection. Ran up the compressor and it pulled -19 in no time. Thanks for your help.
Similar Threads
-
NVQ 3 online test
By Burrah Boy in forum TrainingReplies: 7Last Post: 28-10-2009, 08:35 PM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
DIAGRAMS : Cooling Discharge/Suction pressure vs. Outdoor temp
By psalom in forum DomesticReplies: 0Last Post: 28-08-2007, 09:48 AM -
condensing temp rule of thumb
By angryk in forum FundamentalsReplies: 8Last Post: 14-03-2003, 04:00 AM -
R50 condensing pressure?
By aenigma in forum RefrigerantsReplies: 2Last Post: 06-11-2002, 10:07 AM