    Low condensing pressure on freezer, not pulling temp



    I have a walkin freezer room thats not pulling temp. Got a call last night, freezer was at 3.2C. by the time I got there it was at -13.8. Checked out system. Everything seemed ok. sight glass full. discharge pipe roasting,suction pipe cold,liquid warm, condenser coil clean,evap coil clean. All fans running. Suction pressure 2bar,condensing pressure 11bar. Very little heat rejection from the condenser. Blocked the condenser coil pressure slowly rose to 17.5bar. unit pumped down slowly as well. Condensing unit is Maneurop. Compressor is a NTZ068A4LR1A. Would I be right to say compressor is on its way out? If compressor is gone would I be right in changing it to a Copeland scroll?? Thanks for any help



  2. #2
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: Low condensing pressure on freezer, not pulling temp

    Quote Originally Posted by Crypton View Post
    I have a walkin freezer room thats not pulling temp. Got a call last night, freezer was at 3.2C. by the time I got there it was at -13.8. Checked out system. Everything seemed ok. sight glass full. discharge pipe roasting,suction pipe cold,liquid warm, condenser coil clean,evap coil clean. All fans running. Suction pressure 2bar,condensing pressure 11bar. Very little heat rejection from the condenser. Blocked the condenser coil pressure slowly rose to 17.5bar. unit pumped down slowly as well. Condensing unit is Maneurop. Compressor is a NTZ068A4LR1A. Would I be right to say compressor is on its way out? If compressor is gone would I be right in changing it to a Copeland scroll?? Thanks for any help

    You don't mention the type of refrigerant?
    It is important so we can make a jugement on the comp.

    Have you done a pump test on the thing.

    With gauges fitted front seat the suction service valve and see with the suction does.

    It should go very low into a vac (lower than 15"hg about 20"hg to 30"hg), the lower the better and with the
    comp off it should stay like that for a good few mins (you may need to do somthing to the lp
    switch to allow it to pump into a vac).

    coolrunnings

    .
    Last edited by cool runings; 05-06-2010 at 02:12 AM.

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Low condensing pressure on freezer, not pulling temp

    TEV are designed for a certain pressure drop across the vav to feed liquid to the evaporator, reduce the delta p and you starve the evaporator.

  4. #4
    Join Date
    Jun 2010
    Location
    Oregon
    Posts
    20
    Rep Power
    0

    Smile Re: Low condensing pressure on freezer, not pulling temp

    the ultimate question!
    what is your subcoolin, SC and superheat. SH?
    its a must check.

  5. #5
    Join Date
    Jun 2008
    Location
    NZ
    Posts
    102
    Rep Power
    17

    Re: Low condensing pressure on freezer, not pulling temp

    Hope you've found the cause of your problem.

    Slow pump down sounds like you might have an issue with valves in the comp. Like Cool Runnings said - do the pump-down test.

    If you fit a scroll as a replacement, you may find you have to install other fun stuff like liquid injection for cooling - might make replacing the manuerop with an identical unit more attractive.

  6. #6
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Low condensing pressure on freezer, not pulling temp

    Check the refrigerant amount.

    If the compressor head is roasting then you have very high compression ratio.
    Probably there is not enough gas in the system.
    Cheers
    Even Einstein Asked Questions

  7. #7
    Join Date
    Nov 2008
    Location
    Ireland
    Posts
    55
    Rep Power
    16

    Re: Low condensing pressure on freezer, not pulling temp

    Thanks for the replies. Did the pump down test and the unit barely made it into a vac. Turned off compressor and it never held. It came straight out. I changed the compressor for a copeland scroll with liquid injection. Ran up the compressor and it pulled -19 in no time. Thanks for your help.

Similar Threads

  1. NVQ 3 online test
    By Burrah Boy in forum Training
    Replies: 7
    Last Post: 28-10-2009, 08:35 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Replies: 0
    Last Post: 28-08-2007, 09:48 AM
  4. condensing temp rule of thumb
    By angryk in forum Fundamentals
    Replies: 8
    Last Post: 14-03-2003, 04:00 AM
  5. R50 condensing pressure?
    By aenigma in forum Refrigerants
    Replies: 2
    Last Post: 06-11-2002, 10:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •