    Condenser+Receiver: outdoor installation



    The question is about multycompressor-Rack. We can install receiver under condenser ("scandinavian scheme"). In such case we could spare money for KVR-NRD-System (Danfoss).

    But I've heard there are problems for this variant of installation.
    May be it is because if out temp is too low (-35 Grad C), f.E.?

    Could you explain me?



  2. #2
    Join Date
    Apr 2005
    Location
    Moscow
    Age
    48
    Posts
    20
    Rep Power
    0

    Re: Condenser+Receiver: outdoor installation

    It`s possible but You should insulate the receiver. In any case price for Danfoss kit not so critical.

  3. #3
    Join Date
    Jun 2004
    Location
    Russia
    Age
    57
    Posts
    19
    Rep Power
    0

    Re: Condenser+Receiver: outdoor installation

    condenser+receiver must be at the same out temperature - in other case all R404A (f.E.) will be in condenser.

  4. #4
    Join Date
    Apr 2005
    Location
    Moscow
    Age
    48
    Posts
    20
    Rep Power
    0

    Re: Condenser+Receiver: outdoor installation

    You can install check valve. You should be carefull then you selecting expansoin valve if outside temperature falls to -35 liquid will be very subcooled.

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Condenser+Receiver: outdoor installation

    Hi Andrew,

    You can use a heating tape 30W/M around the reciver to maintain the temp in it.

    Chemi

  6. #6
    Join Date
    Jun 2004
    Location
    Russia
    Age
    57
    Posts
    19
    Rep Power
    0

    Re: Condenser+Receiver: outdoor installation

    Hi Chemi,

    I'm interested very subcooled liquid - if we have so subcooled liquid - in evaporator we have ...

    BR

    Andrew

    PS In Israel you have not such problems? Out temp in Russia can be very low!

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Condenser+Receiver: outdoor installation

    In Israel you have not such problems?
    Hi Andrew,

    -35? in Israel? Never.
    It can go as low as -5°c.
    Weather in general warm to hot and some times' very hot.
    It was yesterday 37°c and today 33 , good for business

    You have to maintain pressure differential between the receiver and the TEV.
    If the differential is too low, the TEV will not function well.

    Heating tape is a good solution, it has to be controlled by a pressure control though.

    Chemi

  8. #8
    Join Date
    Apr 2005
    Location
    Moscow
    Age
    48
    Posts
    20
    Rep Power
    0

    Re: Condenser+Receiver: outdoor installation

    Hi Chemi

    +37C (but +33C not so bad too ) it`s almost perfect weather for our business!
    In my mind most suitable solution is flexible heater with variable impedance and insulation on receiver.

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Condenser+Receiver: outdoor installation

    Look here for examples.



    http://www.labkorea.com/lab/heatingacce.html


    Chemi

  10. #10
    Join Date
    Jun 2004
    Location
    Russia
    Age
    57
    Posts
    19
    Rep Power
    0

    Re: Condenser+Receiver: outdoor installation

    Thanks to all for answers!

    I thought about this problem - we have to do such scheme for our customer and it is not solved.

    I understand the situation - if outer temp is -40 Grad C and we have in condenser+receiver liquid with temp -40 Grad C. And no gas - we can use p-s diagramm and we see - 100% liquid.
    For TX Ventil it is very bad - we have very low pressure and compressor will not work.

    The question - how can we get gas in system - or how can we make the system workable? In compressors are not working for long time - all R404A will be in condenser+receiver in liquid stand. Or not?

  11. #11
    Join Date
    Apr 2005
    Location
    Moscow
    Age
    48
    Posts
    20
    Rep Power
    0

    Smile Re: Condenser+Receiver: outdoor installation

    In my mind you shoud use KVR+NRD or similar.

Similar Threads

  1. method to design air cooled condenser
    By abbasi in forum New Technologies
    Replies: 4
    Last Post: 12-02-2008, 08:34 AM
  2. Condenser outlet lower than receiver inlet?
    By Kevin S in forum Fundamentals
    Replies: 10
    Last Post: 02-05-2006, 06:27 AM
  3. Optimum condenser fan speed
    By star882 in forum Fundamentals
    Replies: 4
    Last Post: 27-02-2006, 01:50 AM
  4. Liquid trap
    By Herschmidt in forum Supermarket Refrigeration
    Replies: 1
    Last Post: 13-08-2005, 11:39 PM
  5. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •