    Prestcold/Copeland unit



    Hi Guys,

    Got called out over the weekend to the following

    Prescold Cond unit AP1ZF 15K Compressor ZF15K4E-TFD-265
    R404 3 phase. Now the prob's start

    From what i can see in the NRS book pg 198 all ZF compressors are rated for low back pressure but this one is running 18ft of dairy/drinks chiller (Setpoint +5)

    Has anyone come accross this before, is this the correct unit/compressor or has someone had one laying about and fitted it

    Regards

    Fatboy



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Prestcold/Copeland unit

    Hi Raymond,

    According to Copeland, this compressor is for medium/low temp with liquid injection Head cooling.

    What is your evaporating temp?

    You can download from Copland web site the compressor calculator, helpful little tool.

    Chemi

  3. #3
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Prestcold/Copeland unit

    hi Chemi,

    yes forgot to add, pot does have liquid injection.

    I would guess evap temp would be around -5 to -10. It runs an OLD !!! Arneg Multideck at a Petrol station and they swap it about often fron a drinks chiller to a dairy case (+3)

    regards

    Raymond
    Last edited by Latte; 10-04-2005 at 06:54 PM.

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Prestcold/Copeland unit

    -5 to -10 ism AC compressor.

    ZF are for low/medium, -30 to - 15 evaporating temp.

    Your compressor is for different application.

    What exactly is the problem with the unit?

    Chemi

  5. #5
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Prestcold/Copeland unit

    Hi Chemi,

    Don't know the history just asked by the office to go in and confirm that the compressor is down. Apparently there have been problems in the past where pot's have been ordered but it turned out not to be the fault when there have been temp problems. This time the compressor has seized.

    Regards

    Raymond

  6. #6
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Prestcold/Copeland unit

    Hi Chemi,

    Just to give you an update, i ended up fitting the same compressor as come off and it seems to be working fine. I have also been to another site for the same company and all their compressors are also ZF units 9 - 15.

    Dont know whats going on and why all this companies units are like that but the brains in my company say it's OK so i will leave it at that.

    Thanks

    Fatboy

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Prestcold/Copeland unit

    If it works fine - don't touch it

    One thing you didn't say, is what is the evaporating temp?

    I think it will be arround -10°c.

    Chemi