Results 1 to 8 of 8
Thread: Armoured cable
    Mar 2004
    624
    21
    Armoured cable
    Hi All
    Is it still within 16th edition regs to use the outer sheath of the armoured cable as the main earth.
    Thanks Bernard
    Jun 2002
    628
    23
    Re: Armoured cable
    Hi. bernard
    Where the cpc or circuit protective conductor (earth) is formed by conduit,trunking,ducting ,or by the metal sheath and or armour of cable ,the earthing terminal of each accessory shall be connected by a seperate protective conductor to an earthing terminal incorporated in the associated box or enclosure.
    In other words continue the earth continuity of the armour with a banjo washer and seperate cpc to the earthing terminal.
    Hope this helps.
    Mark
    Mar 2004
    624
    21
    Re: Armoured cable
    Thanks Mark
    bernard
    artisan's Avatar
    artisan Guest
    Re: Armoured cable
    Quote Originally Posted by bernard
    Hi All
    Thanks Bernard
    You can use the outer steel wire as earth, but only up to a certain size i think its 10mm the you have to run a seperate earth. this is because the cross sectional area of the earth on cables higher then 10mm is less than half of the main conductor
    Jun 2002
    628
    23
    Re: Armoured cable
    Hi.just had time to re-read the regs
    543-02-02 A protective conductor may consist of one or more of the following.
    (i)a single core cable.
    (ii)a conductor in a cable.
    (iii)an insulated or bare conductor in a common enclosure with insulated live conductors.
    (iv)a fixed bare or insulated conductor.
    (v)a metal covering ,for example the sheath,screen or armouring of a cable.
    (vi)a metal conduit or other enclosure or electrically continuous support system for conductors.
    (vii)an extraneous-conductive part complying with regulation 543-02-06
    543-02-03 A protective conductor of the types described in items (i) to (iv) of regulation 543-02-02 and of cross sectional area 10mm or less,shall be of copper.
    Sep 2003
    ISRAEL
    72
    4,248
    Re: Armoured cable
    Hi Mark,
    Don't you guys use the XLPE green cables double insulation?
    I have seen those armoured cables when looking at nice instelation of two cassettes done by Abe.
    These are what we call flaxiable cables and only use them for short connections.
    Supply is by the green XLPE cables with one copper conductor.
    Chemi
    rbartlett's Avatar
    rbartlett Guest
    Re: Armoured cable
    we use this a lot
    http://www.cse-distributors.co.uk/ca...raid-cable.htm
    but for mains i use either swa or
    http://www.pirelli.co.uk/en_GB/cable...fp200_Gold.pdf
    in white
    cheers
    richard
    Jun 2002
    628
    23
    Re: Armoured cable
    Quote Originally Posted by chemi-cool
    Hi Mark,
    Chemi
    Some customers specify armoured cable chemi
  1. Door Heater Tape
    By Abe in forum Commercial
    Last Post: 20-05-2008, 06:38 PM
  2. Cable current carrying capacity
    By Abe in forum Electrical
    Last Post: 25-09-2005, 10:23 PM