Armoured cable
Hi All
Is it still within 16th edition regs to use the outer sheath of the armoured cable as the main earth.
Thanks Bernard
-
31-03-2005, 08:40 PM #2
Re: Armoured cable
Hi. bernard
Where the cpc or circuit protective conductor (earth) is formed by conduit,trunking,ducting ,or by the metal sheath and or armour of cable ,the earthing terminal of each accessory shall be connected by a seperate protective conductor to an earthing terminal incorporated in the associated box or enclosure.
In other words continue the earth continuity of the armour with a banjo washer and seperate cpc to the earthing terminal.
Hope this helps.
Mark
-
31-03-2005, 08:50 PM #3
Re: Armoured cable
Thanks Mark
bernard
-
01-04-2005, 08:45 AM #4
Re: Armoured cable
Originally Posted by bernard
-
01-04-2005, 09:01 PM #5
Re: Armoured cable
Hi.just had time to re-read the regs
543-02-02 A protective conductor may consist of one or more of the following.
(i)a single core cable.
(ii)a conductor in a cable.
(iii)an insulated or bare conductor in a common enclosure with insulated live conductors.
(iv)a fixed bare or insulated conductor.
(v)a metal covering ,for example the sheath,screen or armouring of a cable.
(vi)a metal conduit or other enclosure or electrically continuous support system for conductors.
(vii)an extraneous-conductive part complying with regulation 543-02-06
543-02-03 A protective conductor of the types described in items (i) to (iv) of regulation 543-02-02 and of cross sectional area 10mm or less,shall be of copper.
-
02-04-2005, 08:14 AM #6
Re: Armoured cable
Hi Mark,
Don't you guys use the XLPE green cables double insulation?
I have seen those armoured cables when looking at nice instelation of two cassettes done by Abe.
These are what we call flaxiable cables and only use them for short connections.
Supply is by the green XLPE cables with one copper conductor.
Chemi
-
02-04-2005, 11:54 AM #7
Re: Armoured cable
we use this a lot
http://www.cse-distributors.co.uk/ca...raid-cable.htm
but for mains i use either swa or
http://www.pirelli.co.uk/en_GB/cable...fp200_Gold.pdf
in white
cheers
richard
-
02-04-2005, 06:51 PM #8
Re: Armoured cable
Originally Posted by chemi-cool