    Remote controller set temp



    System: Daikin VRV III
    Cordet remote controller -BRC1C62.
    Ceiling mounted indoor unit is working but the remote controller not shows the set temp (swing ,mode & fan speed display available on display)

    Your Help on this matter is appreciated



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Remote controller set temp

    The set temperature does not show if you select 'Fan Only' mode or 'Dehumidifying' mode.

    Can you see a snow flake or sun symbol at the top of the controller?

  3. #3
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

    Re: Remote controller set temp

    Hello Frank, Indoor unit not in use from previous 12 month.For one 28 hp system there is 13 indoor, out of that one is not in use due to some reason. I found water leakage from unit & wired remote controller not shows the set temp. when I start unit from remote controller, found unit is working & it shows the Swing ,cooling & fan speed symbol. I checked field setting found all the second code numbers are factory set.checked proper connection, any loose contact.
    No other mulfunction error code found on remote controller except "A3".

    Is this possibility 1) Expansion valve is in open condition.since unit is not in use so water drop created on coil fins.automatic drain system also not working. 2) there is problem in PCB card.

    (Before one month Daikin service enginner connect the
    Service checker Instrument to this Unit for diagnosis of another indoor unit problem.Is this problem created due to Daikin service engineer mistake ? because before connecting service checker instrument to this unit we have never seen water leakage & set temp issue in the period of 11 month.At Present we are not taking support from Daikin, warrenty period is over)

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Remote controller set temp

    If there were any faults, the system would be showing an error code. No faults, steady red operation light - no problem.

    The only other time where a wired remote controller does not show a temperature display is when it is connected to a VAM unit only.

    What is the model number of your indoor unit?

  5. #5
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

    Re: Remote controller set temp

    Indoor unit Model no -FXFQ100PVE
    Outdoor Model -RXYQ18PY16 & RXYQ10PY16
    Wired Remote controller -BRC1C62

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Remote controller set temp

    Is the remote controller connected to the P1 P2 terminals as a single controller?

  7. #7
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

    Re: Remote controller set temp

    Yes,remote controller connected to the P1 P2 terminals.

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Remote controller set temp

    Have you tried swapping the controller with a different one on the system?

  9. #9
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

    Re: Remote controller set temp

    I swapped the controller with a different one but found no change in existing problem.

  10. #10
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

    Re: Remote controller set temp

    Hello Frank, Thanks for your cooperation, Today I interchange existing problem unit PCB card with another unit PCB for troubleshooting.When I connect the another PCB card, remote controller shows the set temp & drain pump also work. & again reconnect the previous PCB card found existing problem so conclude PCB card is faulty. Is this correct ? can we solve problem with help of service checker because strange thing is there in no error code on remote controller.

  11. #11
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Remote controller set temp

    That was going to be my next suggestion....the indoor fan coil pcb is faulty..looks like you beat me to it.

Similar Threads

  1. Relocation Of Daikin Remote controller
    By moondawn in forum Air Conditioning
    Replies: 1
    Last Post: 11-12-2009, 09:32 PM
  2. Failing remote controller (daikin BRC1D527)
    By ColocMadrid in forum Air Conditioning
    Replies: 4
    Last Post: 22-06-2009, 08:51 PM
  3. DAIKIN VRV Remote controller
    By 2007eng in forum Air Conditioning
    Replies: 15
    Last Post: 19-07-2008, 07:04 PM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  5. Stiebel Remote Controller?
    By Makeit go Right in forum Air Conditioning
    Replies: 7
    Last Post: 24-05-2006, 12:33 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •