    Koxka Serve overs (evaporator problems)



    Hi all!

    Do any of you have problems with the evaporators on koxka serve overs i have been on quite a few at supermarkets they corrode badly and lose the gas..
    I have noticed if they keep coleslaw in them it seems to eat them away what ever kind of reaction it has..

    Were would be the best place to buy replacement evaps in the uk/N.Ireland.

    Cheers Chris.



  2. #2
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Koxka Serve overs (evaporator problems)

    Hi Chris,

    First of all try Montgomery Refrigeration at Falcon Rd Belfast.
    028 9066 2111 E-mail Sales@montgomeryrefrig.demon.co.uk
    They are the import guys for koxka.

    Secondly you could try Beehive coils in Newmarket but you would probably have to send them the old one but they will make anything.

    Don't know why but Koxka evap are notorious for leaks and soucing parts a nightmare. Rule of thumb normally, if it's an old R12 unit its easier/cheaper to scrap it and get a new one from Fosters or Williams.

    If you can give us more unit details will try and help

    Regards

    Fatboy

  3. #3
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Koxka Serve overs (evaporator problems)

    A prominent problem associated with mostly integrals storing deli,salad ie strong cheeses,salami/sausage,dressing etc is evap leaks on return bend joints etc,(copper becoming pitted)
    It is not only koxxka, all makes suffer,when i get time i will post link to discussion we had about the subject.
    Kind regards.Mark
    Last edited by Mark; 16-03-2005 at 10:36 AM.

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Koxka Serve overs (evaporator problems)

    Its the Strong cheeses and vinegar that causes pitting and eventually holes.

    I had such a problem in a goat cheese maturing room, ammonia was the problem there.

    The third coil was spray painted with epoxy paint, one layer per week, six times.

    Lost a bit of heat exchange but it is running fine for 3 years now.

    Blygold didn't hold over 3 months.

    Another thing is using a SS coil and fins but I'm afraid it cost more then the whole unit.

    Chemi

  5. #5
    Join Date
    Jan 2005
    Location
    N.Ireland
    Age
    48
    Posts
    177
    Rep Power
    20

    Re: Koxka Serve overs (evaporator problems)

    Hi chemi

    Its a pitty the people who make the evaps for serve overs and salad bars wouldnt do this when they are making them.
    I was on a salad bar a while ago which had a gas leak the unit was 2 years old.
    So i got out the leak detector and sure enuf the evap was leaking at one of the bends the copper wasnt exsposed it was covered with grey paint but the was chipped off at that place.

    The copper coils are paper thin the prob is that bat we dont get involved in selling these cabinets (just repair them) as it would end up giving us a bad name.
    But before fitting any new evaps i will take your advice and give them a good spraying in the future.
    Thanks chris.