In supermarket rack systems, I see references to "fast recovery 300 psig." Can anyone tell me what this refers to? It does not have anything to do with refrigerant recovery.
Thanks much,
Christian
-
15-04-2010, 01:36 AM #2
Re: Fast recovery???
You are probably reading this on a controller? If so, then this mean @ 300 the controller will bring the condenser fans on to try and lower the head.
-
15-04-2010, 02:19 AM #3
Re: Fast recovery???
Basically, Brad, you are correct.
Fast recovery is a CPC/Emerson thing. They give you 2 levels of head pressure control.
One that is lower and a little slower. Once you hit the higher 'fast reovery' setpoint, your delays shorten and the fans ramp up faster.
Never completely understood WHY this was available, but there it is.
-
03-05-2010, 03:46 AM #4
Re: Fast recovery???
it is available for systems that dont use discharge xducer by itself to control head. fast recovery goes off of xducer only, while main control may be looking at liquid temp, drop leg pressure, and ambient in some kind of equation to run the unit "more effeciently" the fast recovery is a back up in case the 3-5 sensor control fails somewhere
Similar Threads
-
Is this normal with a CR 700 recovery unit?
By AlexLPD in forum Trouble ShootingReplies: 6Last Post: 13-04-2010, 07:40 PM -
Is Air Content Analyzer Required on Recovery Cylinder?
By A1_Autos in forum Air ConditioningReplies: 9Last Post: 26-03-2010, 07:48 PM -
Can ITE Mini R Recovery Unit recover Liquid?
By A1_Autos in forum Air ConditioningReplies: 8Last Post: 22-03-2010, 11:51 PM -
complete System Recovery
By absolute-zero in forum Computers & the InternetReplies: 9Last Post: 20-01-2008, 06:03 PM -
Refrigerant recovery
By chillyblue in forum Technical DiscussionsReplies: 11Last Post: 23-07-2007, 10:58 PM