Results 1 to 8 of 8
07-04-2010, 12:08 AM #1
Help with selection of evaporator
Dear Guys:
I'm going to install two evaporators (attach specifications of the evaporators) in a process room of 24.5m x 11.5 m x 4.2m (L x W x H) in this procces room will work about 70 people and i'm not sure about the distribution of the evaporators could you help me?
i'm attaching a diagram with two options what is the better ?
Luis.
07-04-2010, 02:40 AM #2
Re: Help with selection of evaporator
Either would work Ok, but air velocity is quite high, so you need to be careful. In option one, you will get very little air rebounding off the end wall, but in option 2 you will.
I would not normally use these types of evaps in a process room, unless connects to ducting or air sock
07-04-2010, 03:33 AM #3
I would advise that you select evaporators with less air throw maybe dual discharge and install them along the width of the room.
the blowers you have selected have to high velocity the further the throw the higher the velocity, in my experience even if the air is directed above the people working you will still have turbulance resulting in drafts and uncomfortable working conditions.
07-04-2010, 02:13 PM #4
Go for a wind sock system. much better for personal comfort.
19-05-2010, 04:54 PM #5
You can use an air sock even if you have only 50Pa to inflate it, the workers will thank you!
19-05-2010, 09:34 PM #6
Based on what you have. I'd put them on the far ends blowing towards each other.
19-05-2010, 11:16 PM #7
I would use option 2 with wind socks.
20-05-2010, 03:34 AM #8
In my experience, it would be better to use 4 smaller evaporators instead of two and I would install them on the length (24m) of the room for better air distribution.
As others mentioned this, if people are in the room and comfort must be observed then it would be better to use a duct system which will give you low noise and better distribution.
cheersEven Einstein Asked Questions
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
EVAPORATOR leaked
By James priyono in forum Air ConditioningReplies: 4Last Post: 23-05-2009, 10:19 AM -
What is the best location for a evaporator fan?
By Jasno999 in forum FundamentalsReplies: 3Last Post: 21-02-2007, 12:34 AM -
Evaporator Selection
By chooipeng in forum NH3Replies: 12Last Post: 26-09-2006, 08:11 AM -
Evaporator Fan Test and Selection
By pcle in forum Trouble ShootingReplies: 0Last Post: 18-11-2003, 03:10 AM